problem with STULZ air conditioner sensors

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • problem with STULZ air conditioner sensors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2024-04-04 11:48 PM

0 Likes
4
2775
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2024-04-04 11:48 PM

problem with STULZ air conditioner sensors

Hello

the return temperature and supply temperature shown in dce.

 

When I associate these sensors to their genome model in DCO, the return temperature and supply temperature are not recovered by DCO and in the graph only humidity temperature is displayed

 

Temperatura de suministro -  Unit supply air temperature

Temperatura de retorno - Unit return air temperature

 

how can I correct the problem

 

Regards.

 

Caroll

 

(CID:131961648)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2024-04-04 11:48 PM

0 Likes
2
2775
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2024-04-04 11:48 PM

Hi Caroll,

The option for entries such as Supply Temperature and Measured Return Temperature in device Properties > Cooling settings:

not designed to get the associated sensor values!

However, the device Properties > External Systems > Devices Sensors:

would show the associated sensor information!

Kind regards

(CID:131961852)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2024-04-04 11:48 PM

0 Likes
2
2776
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2024-04-04 11:48 PM

Hi Caroll,

The option for entries such as Supply Temperature and Measured Return Temperature in device Properties > Cooling settings:

not designed to get the associated sensor values!

However, the device Properties > External Systems > Devices Sensors:

would show the associated sensor information!

Kind regards

(CID:131961852)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2024-04-04 11:48 PM

In response to DCIM_Support
0 Likes
0
2775
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2024-04-04 11:48 PM

Hello Jef

The temperature sensors have been verified in the expert and these are shown.

When I verify in the dco, the capture of these aforementioned devices does not come out, what is missing?

On the other hand in the cabinets if the temperature sensors are shown, send screen

 

Regards

Caroll

(CID:131964035)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2024-04-04 11:48 PM

In response to DCIM_Support
0 Likes
0
2775
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2024-04-04 11:48 PM

Hi Caroll,
If I understand correctly question is why you are not seeing all temperature sensor measurements in DCO, right? If yes, then please see the following page: DCE Sensor Mapping to DCO, it describes the currently supported sensor mapping in DCO. So these Temperature Sensors may be supported:

EXTERNAL_TEMPERATURE

SUPPLY_AIR_TEMPERATURE

RETURN_AIR_TEMPERATURE

INTEGRATED_TEMPERATURE

RACK_INLET_TEMPERATURE

UNIT_TEMPERATURE

Kind regards

(CID:131964284)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2023-10-22 09:34 PM

0 Likes
0
2776
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:45 PM . Last Modified: ‎2023-10-22 09:34 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore