how to configure a Uniflair downflow CRAC with SNMP?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • how to configure a Uniflair downflow CRAC with SNMP?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 PM . Last Modified: ‎2024-04-09 01:35 AM

0 Likes
8
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 PM . Last Modified: ‎2024-04-09 01:35 AM

how to configure a Uniflair downflow CRAC with SNMP?

Hello guys,

I'm trying to integrate an Uniflair downflow CRAC as a SNMP device with  Carel pCOWeb card. I requested a DDF to the multivendor service and after import it I cannot see right values. All values are N/A or -85899,3460. Multivendor said me it's due a bad configuration but I don't know how to configure it.

Accessing with the web browser also can see a right values as you can see in the attached screenshot

Best regards,

 

Enric

(CID:105459931)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

0 Likes
1
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

Hi Enric.

Please find below my suggestions.

1) For the device

In case you see "U"-signs in the Web-interface it is not the problem of the DDF. In general it is the problem of communication between controller (pCO1) and card (pCO-Web). It is also available to check it in the MobBus register table in the "Summary page" (unfortunately can't show it as have no access to web-interface). In case you see U-signs in all cells you definitely have something wrong with controller to card connection   

Double-check communication parameters in the pCO-Web and also in the controller (speed: 19200 and protocol: Standard) with LCD-menu on the CRACK. CRACK rebooting is also will be useful. 

2) TCP Modbus connection

When you will see right data in the Web-interface you can start to integrate devices into the DCE. To use TCP Modbus you need to have ModBus DDF for it. Then delete the device. Add Modbus DDF to DCE. Then make "Add device" ->"ModBus TCP" and point out IP of the device and DDF that DCE should use.

Hope this will help.

(CID:105460015)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

0 Likes
2
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

Hi Enric,

 

There are multiple different Uniflair devices available. There is also an issue with the Carel pCOWeb card. That card re-uses OIDs. The same OID that may be a temperature for one unit could be a pressure OID for another unit. There is also no OID in the card that properly defines what unit you are polling. Due to this, DCE can not tell what unit it is communicating with. If you have more than one Carel DDF or more than one type of device with that card in it, we can not differentiate between the 2 and may use the wrong one.  I strongly suggest using the Modbus feature of the Carel pCOWeb card if that is the case.


If on the other hand, you only have one type of Carel device / Uniflair cooling unit AND you have only 1 Carel DDF, It should work fine. The issue there sounds like it could be the wrong DDF. If you know the OIDs for the different sensors on the device, you can actually open the DDF and look for these values. You can then see what text is associated with that OID. You can manually poll that OID on the device to see if it is pulling these strange numbers from the device itself (device is having the issue) or if the OIDs are incorrect and again, the DDF is the wrong one.


Steve

(CID:105459934)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

In response to DCIM_Support
0 Likes
0
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

Hi Steve, I have different Uniflair devices and maybe the problem is what you say. How can I use the Modbus feature? Regards, Enric

(CID:105459948)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

In response to DCIM_Support
0 Likes
0
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

Hi Enric, I know the uniflair / Carel systems have that option but I do not have one available to provide configuration information. Hopefully there are others on the post here that can assist with that. Pleas note, if you do try to add it as a modbus device, you'll need to delete it as the device it is now AND you will need a modbus specific DDF. Steve

(CID:105459950)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

0 Likes
1
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

Hi Enric Climent,

                          I think problem is in your serial port setting (Baud Rate) put the same value on both side (unit and web page) after that you can able to see the real time monitoring of CRAC unit.

1) Go to unit and set the serial port rate 19200.

2) Then open the web page > Configuration > username & password > pCO Com >  and set the Baud Rate 19200.

 

Regards,

Rana Ajmal

 

 

 

(CID:105459941)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

In response to DCIM_Support
0 Likes
0
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

Hi Rana, The current serial port rate is already 19200. Regards, Enric

(CID:105459947)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

0 Likes
1
2291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:35 AM

Hi Enric.

Please find below my suggestions.

1) For the device

In case you see "U"-signs in the Web-interface it is not the problem of the DDF. In general it is the problem of communication between controller (pCO1) and card (pCO-Web). It is also available to check it in the MobBus register table in the "Summary page" (unfortunately can't show it as have no access to web-interface). In case you see U-signs in all cells you definitely have something wrong with controller to card connection   

Double-check communication parameters in the pCO-Web and also in the controller (speed: 19200 and protocol: Standard) with LCD-menu on the CRACK. CRACK rebooting is also will be useful. 

2) TCP Modbus connection

When you will see right data in the Web-interface you can start to integrate devices into the DCE. To use TCP Modbus you need to have ModBus DDF for it. Then delete the device. Add Modbus DDF to DCE. Then make "Add device" ->"ModBus TCP" and point out IP of the device and DDF that DCE should use.

Hope this will help.

(CID:105460015)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:34 AM

In response to DCIM_Support
0 Likes
0
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2024-04-09 01:34 AM

Thanks Roman, I've set the right speed in the CRACK LCD-Menu and also reboot it. Now I see right values in both web-interface and DCE. Best regards, Enric

(CID:105460118)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2023-10-31 11:04 PM

0 Likes
0
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:02 PM . Last Modified: ‎2023-10-31 11:04 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of