EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:47 PM . Last Modified: 2024-04-04 11:47 PM
Hello
The temperature sensors are associated to each cabinet and it is observed that the exhaust temperature shown in the dco is not the same as that shown in the dce.
Please could you help me with this topic.
Regards
Caroll
(CID:131962099)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:47 PM . Last Modified: 2024-04-04 11:47 PM
Hi Caroll,
The exhaust temperature is the temperature of the air exhausted by a rack. This is a calculated data displayed in Cooling overlay tooltip. Your associated temperature sensors are being displayed in the rack view, as well as in the 3D view (Measured plane).
Kind regards
(CID:131962332)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:47 PM . Last Modified: 2023-10-22 04:33 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.