buenas noches, me pueden informar como realizo esta configuración en DCO.
(CID:147202004)
Posted: 2020-07-05 09:19 PM
This answer was originally posted on DCIM Support by Jef Faridi on 2019-09-04
Hi Raul,
From the power configuration point of view that's unsupported configuration. Currently in DCO, power configuration/modelling starts from UPS or PDU. Furthermore, modelling parallel UPSs are not directly supported, a suggested workaround could be creating a single UPS (with combined capacity).
Kind regards
(CID:148767304)