Hi,
I have changed all devices to HTTPS and SNMPV3 i have re added the devices via V3 amended the device launch settings to HTTPS but when i launch through DCE i get the following error:

but i can web browse and log in with no issues!!
(CID:144312955)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:46 PM . Last Modified: 2024-04-03 02:32 AM
Solved it 😉
after looking through the logs for the rPDU it appears to be auto-configuring IPv6 so disabling this and the launch to device works fine......
Yeay Me hahaha
(CID:144313000)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:46 PM . Last Modified: 2024-04-03 02:32 AM
Solved it 😉
after looking through the logs for the rPDU it appears to be auto-configuring IPv6 so disabling this and the launch to device works fine......
Yeay Me hahaha
(CID:144313000)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:46 PM . Last Modified: 2023-10-22 04:26 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.