aisle containment snap

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
5
396

aisle containment snap

This question was originally posted on DCIM Support by Eric Clark on 2018-08-09


I have an error message - 

The containment system must snap to the equipment in the ends

 

There is no reference to this in the manual.

 

It is also telling me that equipment is sending air in the wrong direction, which is false - must be something wrong with the object assumptions - anyone know how to fix that ? 

(CID:133369503)

Tags (1)
5 Replies 5
DCIM_Support
Picard
Picard
0 Likes
3
396

Re: aisle containment snap

This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-13


Hi Eric,

Apparently the equipment inside the containment system is not completely covered, eg. there might be some gaps at the ends and therefore the notification is suggesting snap to the equipment in the ends. In the following image, I have an illustration of Cold and Hot aisle containment system:

Additional to snap to the ends, please also notice the orientation of the equipment.

And concerning the "equipment is sending air in the wrong direction ",  without information about your setup it is hard to say what might be causing that. It might be (only guessing) due to the orientation of the racks/neighboring racks and/or the mixed orientation of the equipment inside a rack.

Kind regards

(CID:133370657)

DCIM_Support
Picard
Picard
0 Likes
0
396

Re: aisle containment snap

This comment was originally posted on DCIM Support by Eric Clark on 2018-08-13


that yellow caution space indicates that your containment is drawn  so that it extends across your cabinets. 

 

Why ?

 

It doesn't.

when building containment, it is sealed to the side of the cabinet that is being contained. So if hot containment, as shown in the picture below of an APC solution, you seal the BACK side of the cabinets - and contain the back side of the cabinets.

 

You don't build a structure that mounts to the front of the cabinet on each row, extends up and over, encompassing the entirety of the cabinets and the gap between them. Why would you draw it that way ?

I've tried it how you have it though and it does nothing to change the behavior of DCO in any case.

 

(CID:133370950)

DCIM_Support
Picard
Picard
0 Likes
0
396

Re: aisle containment snap

This comment was originally posted on DCIM Support by Jef Faridi on 2018-08-14


Hi Eric,

The yellow space (in 2D) is to illustrate the so-called service area and similar to your image usually would be left unoccupied/unblocked.

Kind regards

(CID:133370965)

DCIM_Support
Picard
Picard
0 Likes
0
396

Re: aisle containment snap

This comment was originally posted on DCIM Support by Eric Clark on 2018-08-14


The cold aisle only "SERVICES" - in the picture above - 2 tiles between the cabinets - 4' presumably.  Not 6 tiles (12 feet) as you have shown in your images. 

A sliding door could require a couple of inches adjacent to the cabinet to slide open, but you could just as easily have a hinged door or a curtain... 

It sounds like there is no reason to draw the containment outside of the contained area. If there is some technical requirement related to Struxureware managing cooling that requires the containment to be drawn beyond the actual contained area boundaries, please explain.

(CID:133371311)

DCIM_Support
Picard
Picard
0 Likes
0
396

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.