adding two devices in DCE with the same hostname

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • adding two devices in DCE with the same hostname
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:15 PM . Last Modified: ‎2024-04-09 02:31 AM

0 Likes
7
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:15 PM . Last Modified: ‎2024-04-09 02:31 AM

adding two devices in DCE with the same hostname

I'm trying to add to DCE two devices which are in a remote location. I'm accessing to the devices using a NAT so I access to the local router. One of them with port 8161 and the other with the port 9161.

When add one of them, cannot add the second and viceversa. Both are getting the same hostname and I supose that can be the problem.

Any suggestion?

Best regards,

 

Enric Climent

 

(CID:104173774)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:15 PM . Last Modified: ‎2024-04-09 02:31 AM

0 Likes
2
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:15 PM . Last Modified: ‎2024-04-09 02:31 AM

Hi Enric,

 

I would absolutely look into the hostname issue. I'm assuming they have different IPs though correct. Look at both the actual IP and the translated IP. Are either of these devices on the private LAN or both public? What devices are you adding, SNMP / NetBotz?

 

Since 2 devices should not have the same hostname on the same network anyway, have you tried renaming one of them? We are talking actual DNS hostnames correct and not the hostname field of the device? Have you tried removing the DNS entries within DCE? I would think that without DNS, the actual hostnames would not matter.

 

Steve

(CID:104173779)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2024-04-09 02:31 AM

In response to DCIM_Support
0 Likes
0
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2024-04-09 02:31 AM

Hi Steve,

Two devices are in a LAN with different IP addresses and hostnames but DCE access to theses devices trhough a public IP address and different ports using NAT.DCE is working with public address only, not with LAN addresses.

Regards,

 

Enric

 

(CID:104173888)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2024-04-09 02:31 AM

In response to DCIM_Support
0 Likes
0
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2024-04-09 02:31 AM

Hi Enric,

Yes, if the 2 devices have the same IP from DCE's point of view, you can not add both. This would be the same if it were the NAT or possibly even LAN IPs. SNMP within DCE does not distinguish between 2 IPs by port, only IP. If the IPs are the same, it will not be allowed.

Steve

(CID:104173889)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2024-04-09 02:31 AM

0 Likes
0
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2024-04-09 02:31 AM

I agree with Enric: at the moment it is impossible to add SNMP-devices with identical IP-addresses to DCE, but, for example, with different "community string". And in my opinion it is the considerable lack of DCE.

Personally I dealt with such problem, when implemented the decision on collaboration of the DCE and SNMP-proxy server for monitoring of non-standard SNMP-devices (with the limited and incomplete version of SNMP-protocol, for example, Emerson Liebert Powerface controllers with HiSNMP adapters). For the solution of this problem it was necessary to up on SNMP-proxy server network aliases. And their quantity was equal to number of SNMP-devices which needed to be connected to monitoring. Thus the DCE server "saw" not one real IP-address SNMP-proxy server, and it is a lot of different virtual IP-addresses (and the problem of adding devices disappears :-).

Very thanks for the support.

(CID:104173837)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2024-04-09 02:31 AM

0 Likes
1
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2024-04-09 02:31 AM

Hi Enric,

 

The only way I know for this to work is to use different IPs. I know of no way getting it to work with your current config and DCE as your setup exists currently. You'd either need to reconfigure the IPs or use a separate DCE server / VM to monitor the second device.

Steve

(CID:104173897)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2024-04-09 02:31 AM

In response to DCIM_Support
0 Likes
0
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2024-04-09 02:31 AM

Thanks Steve,

Do you have plan to support this kind of connections. Really the customer is connecting by dyndns but as this is not supported by DCE, he is doing the connection with the public IP address.

Regards,

 

Enric

 

(CID:104173966)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2023-10-31 10:13 PM

0 Likes
0
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:16 PM . Last Modified: ‎2023-10-31 10:13 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of