Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:01 PM . Last Modified: 2024-04-08 12:21 AM
The NMC is V3.7.2 and I would like to upgrade card. When I select upgrades and apply upgrade the device doesn't show on the device update list. The UPS is a smart-ups 3000XL
(CID:120133142)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:02 PM . Last Modified: 2024-04-08 12:20 AM
Hi Jan,
The SUMX app or the Smart-UPS / Matrix application is the most recent available NMC1 (AP9617/18/19) for the Smart-UPS in the StruxureWare DCE firmware catalog. I just downloaded the most recent and checked:

6.4.6 firmware is only available for the NMC2 cards (AP9630/31/35).
If there is a newer version, it may take a little time to get it into the catalog but until that is done, the only option would be to manually upgrade the cards. At this time however, that seems to be the most current available on the downloads page:

Thanks,
Steve
(CID:120133154)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:02 PM . Last Modified: 2024-04-08 12:20 AM
Hi Jan,
The SUMX app or the Smart-UPS / Matrix application is the most recent available NMC1 (AP9617/18/19) for the Smart-UPS in the StruxureWare DCE firmware catalog. I just downloaded the most recent and checked:

6.4.6 firmware is only available for the NMC2 cards (AP9630/31/35).
If there is a newer version, it may take a little time to get it into the catalog but until that is done, the only option would be to manually upgrade the cards. At this time however, that seems to be the most current available on the downloads page:

Thanks,
Steve
(CID:120133154)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:02 PM . Last Modified: 2024-04-08 12:20 AM
Thanks Steve
(CID:120135675)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:02 PM . Last Modified: 2023-10-22 04:21 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.