Posted: 2020-07-04 10:28 PM . Last Modified: 2024-04-04 03:20 AM
If I have 2 ATS in 1 Rack, I can't config the Power Dependency on one of them.
(CID:134024508)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:28 PM . Last Modified: 2024-04-04 03:20 AM
Hi Carsten,
It is by design only one rack ATS can be connected to a pair of rack pdu's. It is mainly because of the predicted power and power sold estimated load strategies - they treat primary and secondary rack pdu's as if they were paired. One rack pdu cannot be paired multiple times.
Kind regards
(CID:134024526)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:28 PM . Last Modified: 2024-04-04 03:20 AM
Hi,
We have a lot of rack with 2 ATS install and only 2 Rack PDU.
BR
Carsten
(CID:134025773)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:28 PM . Last Modified: 2024-04-04 03:20 AM
Hello
when you talk about ATS, also with Ap771?Because we also have a lot of ATS in racks for mono powered appliances
Best regards
Rocchino
(CID:135432922)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:28 PM . Last Modified: 2024-04-04 03:20 AM
Suggested workaround: Model one ATS with the combined sum of the outlets of all the other ATSs. Connect this ATS to the rack PDUs and the server equipment to the ATS.
Add the other ATSs as "dummy" ATSs, that is without connecting any equipment to them. This way the inventory reports will be valid.
(CID:137103764)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:28 PM . Last Modified: 2023-10-22 04:21 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.