Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Wattage versus kWh readings for UPS

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Wattage versus kWh readings for UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
abrunero
abrunero Cadet
Cadet

Posted: ‎2024-06-17 07:55 AM

0 Likes
2
797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-17 07:55 AM

Wattage versus kWh readings for UPS

Hi. I was asked what is the energy consumption showing through the UPS in a site. This is our own Schneider Electric site Le Vaudreuil in France. I look at each of the 5 UPS monitored at their sensors. From the average of 30 days kWh I read total 17,320 kWh. For the same reading (average over last 30 days) of watts, the total I get is 2,694 Watts. The Watts and kWh readings from the same UPS don't seem to line up. Am I missing something? Thank you!

Labels
  • Labels:
  • IT Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2024-06-17 08:56 AM

1 Like
1
792
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-17 08:56 AM

Hello @abrunero,

 

kWh is an accumulative sensor that continues to increase over time until it is reset.  For this reason, you can not average the kWh sensors and get a true overage usage for the last 30 days, but you have to compare the highest and lowest values to get a delta of increase over the duration of the month.

 

Watts measurement is usually not an accumulative sensor over time.  It is a look at the exact moment in time of what is being consumed. An average of this would show the average of watts used at any point in time over the 30 days.

 

To compare these 2 values you would need to take the delta of kWh (Highest value - lowest value or 30 days ago - current moment) and the average of the watts over the past 30 days and compare them by converting either kWh to watts or watts to kWh.

 

Regards,

Cory

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2024-06-17 08:56 AM

1 Like
1
793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-17 08:56 AM

Hello @abrunero,

 

kWh is an accumulative sensor that continues to increase over time until it is reset.  For this reason, you can not average the kWh sensors and get a true overage usage for the last 30 days, but you have to compare the highest and lowest values to get a delta of increase over the duration of the month.

 

Watts measurement is usually not an accumulative sensor over time.  It is a look at the exact moment in time of what is being consumed. An average of this would show the average of watts used at any point in time over the 30 days.

 

To compare these 2 values you would need to take the delta of kWh (Highest value - lowest value or 30 days ago - current moment) and the average of the watts over the past 30 days and compare them by converting either kWh to watts or watts to kWh.

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

abrunero
abrunero Cadet
Cadet

Posted: ‎2024-06-17 08:59 AM

In response to Cory_McDonald
1 Like
0
791
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-17 08:59 AM

Thanks Cory! Makes sense. I took the average wattage reading from the UPS and calculated the average kWh from there over a period of time. Appreciate the quick response! 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore