Vertical PDU Total power unplugged

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Vertical PDU Total power unplugged
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:30 AM . Last Modified: ‎2024-04-05 02:57 AM

0 Likes
4
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:30 AM . Last Modified: ‎2024-04-05 02:57 AM

Vertical PDU Total power unplugged

Hi ,

We have Vertical PDU AP8886 showing sensor values in DCE report but i cannot see Total Power Output & showing as unplugged. I can see now as new sensor value as " Total Real Power". Before i use to get Total Power Output and now as unplugged.

Can any one have idea on why this is happening.

(CID:128747360)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 AM . Last Modified: ‎2024-04-05 02:57 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 AM . Last Modified: ‎2024-04-05 02:57 AM

Dear Shaik Mahboob Ali,

If this is the reasons then sensor data field should be an identical mapping and it should not have loss of data , what if i need to fetch the data before updates and after updates in my report then my result reports are not accurate from DCE.
In any case proper data mapping should be done to avoid reporting issue with existing sensor data to new sensor data.

I understand this perfectly, but often this requirement, when developing updates to DDF-files or firmware devices, is very difficult to perform or impossible to do at all.

But we need a solution to fetch reports along with old data and new data ?

Many DCE customers, including myself, often asked themselves a similar question. The solution to this problem was perfectly described in topic .

I.e., in your case, in order to avoid such problems in the future, it is necessary to create a Virtual Sensor Total Power (W). This virtual sensor should consist of two device sensors Total Power Output (W) and Total Real Power (W). The problem is only, that the data history of this virtual sensor will start only from the moment it was created. And accordingly, the data history in the past for this virtual sensor will be unavailable.

I hope this is what you need.

With respect.

(CID:128747584)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:30 AM . Last Modified: ‎2024-04-05 02:57 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:30 AM . Last Modified: ‎2024-04-05 02:57 AM

Dear Shaik Mahboob Ali,

In this case there may be two independent reasons why it happened.

Reason 1: the most likely is the update of the version of the DCE software, which resulted in the update of the corresponding native DDF-files.
Reason 2: sometimes this happens also after the device firmware update.

I think it will help you understand why this happened.

If there are more questions, please ask.

With respect.

(CID:128749446)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 AM . Last Modified: ‎2024-04-05 02:57 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 AM . Last Modified: ‎2024-04-05 02:57 AM

Hi ,

If this is the reasons then sensor data field should be an identical mapping and it should not have loss of data , what if i need to fetch the data before updates and after updates in my report then my result reports are not accurate from DCE.

In any case proper data mapping should be done to avoid reporting issue with existing sensor data to new sensor data.

But we need a solution to fetch reports along with old data and new data ?

(CID:128749444)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 AM . Last Modified: ‎2024-04-05 02:57 AM

0 Likes
0
867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 AM . Last Modified: ‎2024-04-05 02:57 AM

Dear Shaik Mahboob Ali,

If this is the reasons then sensor data field should be an identical mapping and it should not have loss of data , what if i need to fetch the data before updates and after updates in my report then my result reports are not accurate from DCE.
In any case proper data mapping should be done to avoid reporting issue with existing sensor data to new sensor data.

I understand this perfectly, but often this requirement, when developing updates to DDF-files or firmware devices, is very difficult to perform or impossible to do at all.

But we need a solution to fetch reports along with old data and new data ?

Many DCE customers, including myself, often asked themselves a similar question. The solution to this problem was perfectly described in topic .

I.e., in your case, in order to avoid such problems in the future, it is necessary to create a Virtual Sensor Total Power (W). This virtual sensor should consist of two device sensors Total Power Output (W) and Total Real Power (W). The problem is only, that the data history of this virtual sensor will start only from the moment it was created. And accordingly, the data history in the past for this virtual sensor will be unavailable.

I hope this is what you need.

With respect.

(CID:128747584)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 AM . Last Modified: ‎2023-10-22 04:14 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 AM . Last Modified: ‎2023-10-22 04:14 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of