Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:30 PM . Last Modified: 2024-04-05 12:32 AM
UPS rebooting every 2 weeks at the same time. Logs only show a network interface coldstarted. I set the self test schedule to never after the last occurance and it happened again. Any ideas?
(CID:129409369)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:30 PM . Last Modified: 2024-04-05 12:32 AM
Hi Todd,
For more specific UPS support, you can also use the forms at http://forums.apc.com as they usually deal with things not DCO and DCE.
Looking at the logs you've provided, it appears that the UPS has a low battery. It is in a constant state of discharge. You may want to look at things like battery age as well as UPS load.
If the battery is indeed bad and the ups goes to battery even momentarily, as the messages indicate it may simply turn off. If it is not happening on the self test, there may simply be a blip in the power that is causing this.
If it is just the network card cold starting and the UPS and it's load are not actually turning off, you may want to have a look at k-base FA156063. This outlines the reasons for warmstarts and coldstarts and has resolutions for both.
Steve
(CID:129409382)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:30 PM . Last Modified: 2024-04-05 12:32 AM
Hi Todd,
For more specific UPS support, you can also use the forms at http://forums.apc.com as they usually deal with things not DCO and DCE.
Looking at the logs you've provided, it appears that the UPS has a low battery. It is in a constant state of discharge. You may want to look at things like battery age as well as UPS load.
If the battery is indeed bad and the ups goes to battery even momentarily, as the messages indicate it may simply turn off. If it is not happening on the self test, there may simply be a blip in the power that is causing this.
If it is just the network card cold starting and the UPS and it's load are not actually turning off, you may want to have a look at k-base FA156063. This outlines the reasons for warmstarts and coldstarts and has resolutions for both.
Steve
(CID:129409382)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:30 PM . Last Modified: 2023-10-22 04:08 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.