UPS Communication alarm

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • UPS Communication alarm
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:32 AM . Last Modified: ‎2024-04-10 01:28 AM

0 Likes
8
2459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:32 AM . Last Modified: ‎2024-04-10 01:28 AM

UPS Communication alarm

Hi,

I have a Struxureware Central 7.0.0 install - most all my PDU, and Cooling devices are on a private network, we have moved our UPS ( a PX250 ) from the private network 192.168.x.x. network to our mgmt. network.

The appliance is also on the MGMT network and that is how we access Struxureware Central.

We get an alarm that Communication with the UPS has been lost, but we can right click on the UPS and launch to it, as well as see all the settings. In DeviceView I have the correct IP address on the MGMT network showing up under hostname.

My questions are:

How do I resolve the error?

We only have one network card in the UPS and it needs to be on the MGMT network so we can do remote server shutdowns.

We do not show any sensor values showing up if I view the device sensors

 

(CID:89555801)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:33 AM . Last Modified: ‎2024-04-10 01:28 AM

0 Likes
2
2459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:33 AM . Last Modified: ‎2024-04-10 01:28 AM

Hi Dave,

 

Is this the only device you have on your network on the public LAN? If not, have you tried another device to see if the same behaviour exists, so we can isolate it, to this UPS?  Does the device come up as failure on DCE under status? Is it a constant UPS Communication Alarm? Are you able to ping the UPS successfully from your laptop without using DCE?  

 

Are you now having trouble discovering the device after deleting it? If so, it might have to do with incorrect SNMP community names. Usually if you can launch to a device and also right click to view the device sensors they might shown something along the lines of sensor value "unplugged". Is this what you were seeing initially? 

 

I would advise that you check the SNMP community names (I would leave these as the default for testing purposes public/private) that you are using to discover the device on DCE and the SNMP access control on the device itself matches up. If they don't match up, you will not be able to discover the device, if these SNMP community names changed on the device, it will show a failure status and the UPS will be in a lost communication state, although you are still able to launch to the device. I would also for testing purposes leave the NMS IP/Hostname to 0.0.0.0 (this is on the web interface of the NMC). Make sure that the port you are using is the correct one and that it is not blocked. 

 

There is a KBase that is very helpful for troubleshooting SNMP problems. The KBase umber is FA226273. The KBase link is below for your convenience: 

http://www.apc.com/site/support/index.cfm/faq/

 

If the above KBase does not help you may need to give us more information on the way your network is set up. Do you have a network diagram that you could possibly send on to us? I would also request the config.ini file from the NMC itself and also the capture logs from the server. To get these, type in the following in a web browser /capturelogs. A packet capture might also be helpful here. 

 

Just an FYI, we are currently on DCE 7.2.4. If you have a software support contract, I would advise that you contact technical support for the upgrade links to the newer version of DCE. 

 

Hope this helps. 

 

Regards,

B

(CID:89556737)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:32 AM . Last Modified: ‎2024-04-10 01:28 AM

0 Likes
0
2459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:32 AM . Last Modified: ‎2024-04-10 01:28 AM

Hi Dave, I assume you have already deleted the old devices and readd'ed using the new ip? Otherwise I would recommend doing so to make sure the device is correctly rediscovered by DCE. It might also be worth trying to do it one more time of only done once. If that doesn't solve the issue I would think the error might be found in the timeout settings on the connection to the device. The network answer time might change slightly going from one network segment to another. It is possible to edit the SNMP scan settings (timeout) for the specific device. This can be done using the menu “Device->SNMP Device communication settings->Device Scan Settings” in the table locate the failing UPS and click bottom right button “Edit Device Scan Settings”. The menu will allow you to increase the timeout value.

(CID:89555845)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:32 AM . Last Modified: ‎2024-04-10 01:28 AM

0 Likes
0
2459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:32 AM . Last Modified: ‎2024-04-10 01:28 AM

Tried those suggestions - one thing to note, the UPS is now on the public LAN side of the StruxureWare Central server, not on the private side. Can it still be discovered? Do I need to have 2 network management cards in the UPS? One to shut down servers on my management network, and another so it can report into StruxureWare Central? Add your comment here...

(CID:89556682)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:32 AM . Last Modified: ‎2024-04-10 01:28 AM

0 Likes
0
2459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:32 AM . Last Modified: ‎2024-04-10 01:28 AM

Hi Dave, It should be fine with one interface card in the UPS and also fine to discover the UPS on the public LAN. Still seeing the communication error issue I guess? Are there any restrictions on the public LAN in terms of traffic or ports that are not allowed?

(CID:89556684)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:32 AM . Last Modified: ‎2024-04-10 01:28 AM

0 Likes
0
2459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:32 AM . Last Modified: ‎2024-04-10 01:28 AM

Yes, still no communication - I have tried both SNMP v1 and SNMP v3 discoveries with no luck after I removed the device. I can hit the UPS admin web interface directly from my machine on the MGMT network. When I had it defined before I deleted it I could even right click and launch to it.

(CID:89556722)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:33 AM . Last Modified: ‎2024-04-10 01:28 AM

0 Likes
2
2460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:33 AM . Last Modified: ‎2024-04-10 01:28 AM

Hi Dave,

 

Is this the only device you have on your network on the public LAN? If not, have you tried another device to see if the same behaviour exists, so we can isolate it, to this UPS?  Does the device come up as failure on DCE under status? Is it a constant UPS Communication Alarm? Are you able to ping the UPS successfully from your laptop without using DCE?  

 

Are you now having trouble discovering the device after deleting it? If so, it might have to do with incorrect SNMP community names. Usually if you can launch to a device and also right click to view the device sensors they might shown something along the lines of sensor value "unplugged". Is this what you were seeing initially? 

 

I would advise that you check the SNMP community names (I would leave these as the default for testing purposes public/private) that you are using to discover the device on DCE and the SNMP access control on the device itself matches up. If they don't match up, you will not be able to discover the device, if these SNMP community names changed on the device, it will show a failure status and the UPS will be in a lost communication state, although you are still able to launch to the device. I would also for testing purposes leave the NMS IP/Hostname to 0.0.0.0 (this is on the web interface of the NMC). Make sure that the port you are using is the correct one and that it is not blocked. 

 

There is a KBase that is very helpful for troubleshooting SNMP problems. The KBase umber is FA226273. The KBase link is below for your convenience: 

http://www.apc.com/site/support/index.cfm/faq/

 

If the above KBase does not help you may need to give us more information on the way your network is set up. Do you have a network diagram that you could possibly send on to us? I would also request the config.ini file from the NMC itself and also the capture logs from the server. To get these, type in the following in a web browser /capturelogs. A packet capture might also be helpful here. 

 

Just an FYI, we are currently on DCE 7.2.4. If you have a software support contract, I would advise that you contact technical support for the upgrade links to the newer version of DCE. 

 

Hope this helps. 

 

Regards,

B

(CID:89556737)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:33 AM . Last Modified: ‎2024-04-10 01:28 AM

In response to DCIM_Support
0 Likes
0
2459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:33 AM . Last Modified: ‎2024-04-10 01:28 AM

Hi Dave, I also noticed you commented on needing 2 NMC's (one for the private LAN and the other for the public LAN to shutdown remote servers). Are you using PCNS? There is an app note on the below link that outlines the communication process of PCNS. http://www.apcmedia.com/salestools/TDOY-5UQVBV/TDOY-5UQVBV_R4_EN.pdf Is the only reason why you are putting the UPS on the public side is for remote server shutdown? Basically it shouldn't matter if the PCNS agent is communicating on the private LAN with an NMC on the public side. As long as the NMC can route the UDP packets to the PCNS agent, and that PCNS can connect to the NMC over HTTP/HTTPS. If there are comms issues by doing this, it would come down to a router/firewall configuration issue.

(CID:89556760)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:33 AM . Last Modified: ‎2024-04-10 01:28 AM

In response to DCIM_Support
0 Likes
0
2459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:33 AM . Last Modified: ‎2024-04-10 01:28 AM

Yes, I could ping it from my laptop. I went thru and checked the community names - they were default. I tried both V1 and V3 discovery last week and no luck One thing I did last week toward the end of my troubleshooting was allow the NMS IP to get a DHCP address and then try to discover on that address. It still did not work. Today I went back thru and changed the NMS address back to 0.0.0.0 as it was last week and as you talked about in your email. I then tried to run the discovery again and this time it did discover. Don't know why toggling that worked but it is back in and reporting fine now so I am happy. Thanks to both you and Soren for providing troubleshooting hints!

(CID:89556787)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 08:33 AM . Last Modified: ‎2023-10-31 11:41 PM

0 Likes
0
2459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 08:33 AM . Last Modified: ‎2023-10-31 11:41 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of