Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Posted: ‎2020-04-16 07:06 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-04-16 07:06 PM
Hi,
We have a DCE VM server with 3000 nodes (Enterprise version), also have created a second server as DR/UAT/DEV server, which is trial mode, with no licenses.
Being that the keys are locked to a MAC address, how would someone recover a server to a new or alternate DR server?
Presume you could request for new keys from Schneider, but this is not a fast process that can be done in DR recovery process.
Only option I can think of would be to create a copy of the VM image, and restore to a new VM, as the MAC is virtual.
Thanks,
David.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-04-21 09:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-04-21 09:20 AM
You can change DR VM MAC address to match the Prod VM MAC, but only if the Prod Mac is removed or not on the network. Then re-apply your Lic Keys to the DR server.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-04-21 09:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-04-21 09:20 AM
You can change DR VM MAC address to match the Prod VM MAC, but only if the Prod Mac is removed or not on the network. Then re-apply your Lic Keys to the DR server.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-04-21 10:41 PM
Thanks, 🏆
I guessed that was the only option. 👍
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.