How do I change temperature sensor value to Degree Celsius in DCO. Currently it is showing Fahrenheit. The temp/humidity sensor is directly connected to RPDU.
(CID:93193758)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:42 AM . Last Modified: 2024-04-10 01:08 AM
Hi Shemilusman,
The temperature can be changed by the settings for the client.
It is found in the menu item "preferences->General" where you should chose "Metric" as system of measurement.
(CID:93193817)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:42 AM . Last Modified: 2024-04-10 01:08 AM
Hi Shemilusman,
The temperature can be changed by the settings for the client.
It is found in the menu item "preferences->General" where you should chose "Metric" as system of measurement.
(CID:93193817)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:42 AM . Last Modified: 2023-10-31 11:38 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.