Temperature threshold maximum limit

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Temperature threshold maximum limit
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
jzurera
Lt. Commander jzurera
Lt. Commander

Posted: ‎2020-05-04 06:30 AM

1 Like
4
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-04 06:30 AM

Temperature threshold maximum limit

Hi team,

 

I am trying to configure a temperature treshold alarm for a compressor, but the maximum value that DCE supports it is 50ºC, and the compressor reaches more than 80ºC. Is there anyway to configure this type of tresholds?

 

Regards

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2020-05-04 07:52 AM

0 Likes
3
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-04 07:52 AM

Hello jzurera,

 

Temperature values are currently restricted to -40-122F as you have already realized.  Depending on the DDF currently being used for your device (RFC, Default, custom, etc)  you may be able to have the sensor changed to be from Temperature to "Other Numeric" which does not have the restriction of min and max values.

 

Submit a ticket here, with as much information as you can about the DDF, device sensor, and that you would like the value changed from Temperature to Other Numeric, and the DDF team will investigate if it is possible in your circumstance:

https://helpcenter.ecostruxureit.com/hc/en-us/requests/new?ticket_form_id=360000111657

 

Possible Information to provide:

- Copy of DDF, if you know what one is being used.  (can be pulled from a DCE backup directory)

- Exact name of the sensor

- That you want it changed from Temperature to Other Numeric

- Screenshot of all DDFs and their versions (depending on if the device is SNMP or Modubs) from:

     - SNMP: Device > SNMP Device Communication Settings > Device Definition Files

     - Modbus: Device > Modbus Device Communication Settings > Device Definition Files.

 

I have submitted an enhancement request for an increase in the temperature range to be increased.  I can not say when or if an increase in the range of the threshold values could be implemented.

 

Regards,

Cory

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2020-05-04 07:52 AM

0 Likes
3
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-04 07:52 AM

Hello jzurera,

 

Temperature values are currently restricted to -40-122F as you have already realized.  Depending on the DDF currently being used for your device (RFC, Default, custom, etc)  you may be able to have the sensor changed to be from Temperature to "Other Numeric" which does not have the restriction of min and max values.

 

Submit a ticket here, with as much information as you can about the DDF, device sensor, and that you would like the value changed from Temperature to Other Numeric, and the DDF team will investigate if it is possible in your circumstance:

https://helpcenter.ecostruxureit.com/hc/en-us/requests/new?ticket_form_id=360000111657

 

Possible Information to provide:

- Copy of DDF, if you know what one is being used.  (can be pulled from a DCE backup directory)

- Exact name of the sensor

- That you want it changed from Temperature to Other Numeric

- Screenshot of all DDFs and their versions (depending on if the device is SNMP or Modubs) from:

     - SNMP: Device > SNMP Device Communication Settings > Device Definition Files

     - Modbus: Device > Modbus Device Communication Settings > Device Definition Files.

 

I have submitted an enhancement request for an increase in the temperature range to be increased.  I can not say when or if an increase in the range of the threshold values could be implemented.

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

jzurera
Lt. Commander jzurera
Lt. Commander

Posted: ‎2020-05-05 03:08 AM

In response to Cory_McDonald
0 Likes
2
1739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-05 03:08 AM

Hi @Cory_McDonald,

 

I think it would be better if this restriction could be changed in DCE, because it will help more people, if we change this DDF it will only be effective for this sensor. I have seen that I can check the pressure in the compressor instead of the temperature and define a numeric threshold alarm over this sensor, so I think it would be faster than create a new DDF for this device.

 

But if in a future we maximum range for temperature could be upgraded to 100ºC for example, it would be very useful for more users.

 

Thanks for your support.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2020-05-05 05:40 AM

In response to jzurera
1 Like
1
1737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-05 05:40 AM

Hello @jzurera,

 

I have already notified product management of the request so it can be looked at for possible addition to the product road-map.  Thanks for the update and I am glad that you found an alternative value to create a threshold against as a workaround.

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2020-05-09 07:08 PM

In response to Cory_McDonald
0 Likes
0
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-09 07:08 PM

@jzurera,

 

Please provide the make/model of the device and a copy of the current DDF if it is a custom DDF.  I would like to add this to the enhancement request.

 

Thank you,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore