SW Portal needs service restart

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • SW Portal needs service restart
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

0 Likes
7
951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

SW Portal needs service restart

Hi All,

 

SW Portal does not run efficiently. I can not access each time that i want. So i restart the service then portal is running. What is that reason? It is a configuration problem or other?

 

Regards

Kerem

(CID:105467327)

Labels
  • Labels:
  • Portal
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

Hi Kerem, Can you please share some details about the installation & server specs? is it a dedicated server? when do see the issue, after the machine has been restarted? Kind regards

(CID:105467778)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

Hi Jef, It is dedicated server. I shared system information in attach. That issue has seen since installed the portal exe. While i am configuring, system is down then i restart the service it is run normally. Regards Kerem

portal System inf.jpg

(CID:105467792)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

Kerem, Does your StruxureWare Portal server run any advanced antivirus tools or software? I have seen cases where antivirus tools can cause performance issues with portal as portal uses many small files and it can also effect the database. If you are able to test, please temporarily disable the antivirus tools to see if the portal behaves properly. If it does, you will need to exclude the portal installation directory and postgres database folders. Regards Greg Sterling

(CID:105467826)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

Hi Greg, Thanks for answer but, Sw Portal does not run with any antivirus tools. So, do you have any other suggestion for me? Regards Kerem

(CID:105467934)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

Hi Kerem, Based on the issue description, it might be memory related problem. I can check your logs files if you wish, if so, please collect the files and share with me (I will send you an invite to my =S= box shortly). The following page describes how to collect the logs file: https://dcimsupport.apc.com/questions/105458527/how-to-collect-struxureware-portal-server-logs Kind regards

(CID:105468014)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2024-04-09 12:53 AM

Hi Kerem, Many thanks for sharing the logs. There was no indication in the log files that should affect the (Portal) server performance. Perhaps after all, it might be memory related, if possible I would recommend the current RAM (4Gb) to be increased. When experiencing "portal not running efficiently", it would be interesting to see/watch the Windows server "Performance" activity (in windows task manager) , specially looking at the Memory usage profile. Kind regards

(CID:105468601)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2023-10-31 11:37 PM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 AM . Last Modified: ‎2023-10-31 11:37 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore