SNMP communities and security considerations for ITE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • SNMP communities and security considerations for ITE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Andy
Andy Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2020-05-18 02:24 PM

0 Likes
5
3817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-18 02:24 PM

SNMP communities and security considerations for ITE

Hello all,

I've got a couple of questions from a customer who seriously care about security.

First: is it possible to avoid from using WRITE community in Gateway settings to not allow any (including SE's) applications any possible chance to change settings. What is the official recommendation?

Second: Some devices in a big data center have only TWO different READ communities. One is used for DCE, another is for a BMS system. It's undesirable to share communities between systems. What is the official recommendation to connect the equipment to ITE Gateway securely?

Thanks.

Labels
  • Labels:
  • IT Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jake_H
Ensign Jake_H Ensign
Ensign

Posted: ‎2020-05-26 06:34 AM

3 Likes
3
3757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-26 06:34 AM

Hi Andy,

The recommended way to connect to the Gateway is with SNMPv3 because it is encrypted and has more secure authentication.  If a device does not support SNMPv3, and therefore must use SNMPv1, you can enter an incorrect WRITE community string.  As of the current version of IT Gateway (1.8), the only time it writes to a device is to register for traps on APC devices which use the NMC network card.  In which case, you can manually register the Gateway as a trap receiver in the NMC's UI.  The Gateway also does SNMP writes to register for event log and waveform information from APC Galaxy VS/VM UPSs.  SNMP writes may be used in future versions of the Gateway to support other features.

 

And of course, the devices should be on a private network.  A little more on that here:  https://helpcenter.ecostruxureit.com/hc/en-us/articles/360007479438-EcoStruxure-IT-Gateway-in-a-Secu...

 

Hope that helps.

 

Jake

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Jake_H
Ensign Jake_H Ensign
Ensign

Posted: ‎2020-06-03 11:49 AM

In response to Andy
0 Likes
0
3718
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-03 11:49 AM

Hi Andy,

Currently (GW version 1.8.x) and previous does not receive traps from 3rd party devices.  We are working on that however, so it may be available in the future.  FTP is used for both firmware updates and for device configuration.  

 

Thanks,

Jake

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2020-05-26 01:09 AM

1 Like
0
3781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-26 01:09 AM

Hi Andy,

 

Thank you for posting and sorry for the delay!

 

I'll see if I can get some eyes on this.

 

Thanks,

 

Stine

Reply

Link copied. Please paste this link to share this article on your social media post.

Jake_H
Ensign Jake_H Ensign
Ensign

Posted: ‎2020-05-26 06:34 AM

3 Likes
3
3758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-26 06:34 AM

Hi Andy,

The recommended way to connect to the Gateway is with SNMPv3 because it is encrypted and has more secure authentication.  If a device does not support SNMPv3, and therefore must use SNMPv1, you can enter an incorrect WRITE community string.  As of the current version of IT Gateway (1.8), the only time it writes to a device is to register for traps on APC devices which use the NMC network card.  In which case, you can manually register the Gateway as a trap receiver in the NMC's UI.  The Gateway also does SNMP writes to register for event log and waveform information from APC Galaxy VS/VM UPSs.  SNMP writes may be used in future versions of the Gateway to support other features.

 

And of course, the devices should be on a private network.  A little more on that here:  https://helpcenter.ecostruxureit.com/hc/en-us/articles/360007479438-EcoStruxure-IT-Gateway-in-a-Secu...

 

Hope that helps.

 

Jake

Reply

Link copied. Please paste this link to share this article on your social media post.

Andy
Andy Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2020-05-28 08:07 AM

In response to Jake_H
0 Likes
2
3751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-28 08:07 AM

Hi Jake, thanks for the detailed answer.

I have proposed to the customer to use a wrong write community. Their answer was 'please make the field unnecessary because the way how it works guides users to make systems less secure'

Can you please help me with other questions closely related to the subject and the PoC at a customer premise.

- manually register the Gateway as a trap receiver - does GW receive and react to Traps/Informs from 3rd party equipment?

- is FTP used for mass APC configuration or SNMP?

- which protocols used for FW upgrades?

 

Appreciated/Andrey

Reply

Link copied. Please paste this link to share this article on your social media post.

Jake_H
Ensign Jake_H Ensign
Ensign

Posted: ‎2020-06-03 11:49 AM

In response to Andy
0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-03 11:49 AM

Hi Andy,

Currently (GW version 1.8.x) and previous does not receive traps from 3rd party devices.  We are working on that however, so it may be available in the future.  FTP is used for both firmware updates and for device configuration.  

 

Thanks,

Jake

Reply

Link copied. Please paste this link to share this article on your social media post.

Jake_H
Ensign Jake_H Ensign
Ensign

Posted: ‎2020-06-23 03:55 PM

In response to Andy
0 Likes
0
3618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-23 03:55 PM

Hi Andy,

An update on the question about traps for third party devices.  We do have limited support for it now.  See this article for more details.  https://helpcenter.ecostruxureit.com/hc/en-us/articles/360009699437-Trap-receiver-registration-for-t...

 

When we receive a trap from the third party device, it will trigger a poll of the configured sensors and alarms.  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore