SNMP Device Scan Settings Priority Scanning with Netbotz 200

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • SNMP Device Scan Settings Priority Scanning with Netbotz 200
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

0 Likes
8
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

SNMP Device Scan Settings Priority Scanning with Netbotz 200

The Priority scanning doesn't appear to work with the netbotz 200.

I have configured snmp traps to the dce server (7.5.0), but alerts only appear at the next poll interval (set to 5 minutes).

Other devices configured for Priority Scanning alert from DCE withing seconds rather than at the next poll.

Is this a limitation of the netbotz 200's? 

 

There is a trap test function on the netbotz, but no way to see if it was received by DCE.

(CID:130682085)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

Dear Mark,

For me this is a long-known problem, the solution of which I know, but I do not know the reasons for its occurrence πŸ˜€. The solution to this problem can be found in my post .

To begin with, I highly recommend that you download the config.ini file from your problematic device and examine its section [SecureInterface]. Is there an IP-address for your target DCE-server in this section?

I will be interested in your answer.

With respect.

(CID:130682250)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

Thanks for the response.

 

I didn't do the initial DCE server setup and devices have only been manually added since.

 

So does access disabled in this mean it is turned off ?

The CurrentAISubscriber is correct.

is the TrapPort the source or destination port? there are firewalls in the network between these.

 

My other Netbotz 200 appears to do the traps as notifications are fast.

There are two more Netbotz 250's that are also not working as expected.

 

Mark.

 

 

[SecureInterface]
; APC Secure Interface (ASI): 
; To add an ASI trap recipient, list the IP address in the following form:
; :,
; CurrentASISubscriber=192.168.0.1
; To remove an ASI trap recipient, list the IP or DNS name using the keyword:
; RemoveASISubscriber=192.168.0.2
; To remove all ASI trap recipients, use the keyword, value pair:
; RemoveALLASISubscribers=yes
Access=disabled
AuthenticationPhrase=APC ASI auth phrase
EncryptionPhrase=APC ASI crypt phrase
TrapPort=9952
CurrentASISubscriber=192.168.1.53:162, ISX Manager

(CID:130682864)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

Dear Mark,

Judging by your config.ini, you are all set up correctly, because only one line is important for this:

CurrentASISubscriber=192.168.1.53:162, ISX Manager

All other lines in your case do not matter.

My other Netbotz 200 appears to do the traps as notifications are fast.

I.e., all your NetBotz-200 devices already work correctly with priority scanning? I.e., do all of your NetBotz-200 devices have the above line in the config.ini file? Did I understand you correctly?

There are two more Netbotz 250's that are also not working as expected.

I want to note, that NetBotz-200 and NetBotz-250 are very different devices from different generations. And yet, did you check the config.ini files for the presence of the above line for all your NetBotz-250 devices of the new generation?

With respect.

(CID:130682980)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

Hi Spezialist,

Many thanks for your expert help.

With guidance from you posts on sorting this with an ATS, and inspecting the config.ini, I seem to have it working better on at least one. They all monitor generators via dry contacts, so I have to wait until a scheduled test to see if it has changed. An snmp set is an easy way to get the entry in. 

One thing that isn't configured on most of my devices is snmp writes. Enabling this and adding snmp trap entries enabled priority scanning for APC UPS's, but not the netbotz.

 

Thanks again,

 

Mark.

 

(CID:131336984)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

Dear Mark,

It's nice to hear that it helped you πŸ˜€.

One thing that isn't configured on most of my devices is snmp writes. Enabling this and adding snmp trap entries enabled priority scanning for APC UPS's, but not the netbotz.

I do not understand why you can not do with NetBotz devices. I, for example, have no problems with NetBotz-200 devices.

Concerning the NetBotz-250 devices I can not say anything: these are devices of another generation. Therefore, you need to first clarify with which NetBotz devices you have problems?

With respect.

(CID:131337097)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:08 PM . Last Modified: β€Ž2024-04-05 12:01 AM

Both Netbotz 200 and 250. Chnages have been made and I'll have them all tested again in the next few weeks.

 

(CID:131959240)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:09 PM . Last Modified: β€Ž2024-04-05 12:01 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:09 PM . Last Modified: β€Ž2024-04-05 12:01 AM

Dear Mark,

Tell us, please, could you solve your problem or not?

With respect.

(CID:131962922)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:09 PM . Last Modified: β€Ž2023-10-22 03:49 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:09 PM . Last Modified: β€Ž2023-10-22 03:49 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.