Hi
i am configuring EE and i cannot see any racks under FMPDU. please help me why i cant see any rack under FMPDU in EE editor? snapshot is attached for your review.
UPS Symmetra 160KW with PDUM160H-B
Rack PDU AP8853
Your as usual support will help me to close this EE chapter.
(CID:110004012)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:33 AM . Last Modified: 2024-04-08 04:08 AM
The racks are not shown in the Energy System view. This is by design. You will configure the power consumption from the racks by using the IT Load script.
-- Christian
(CID:110004016)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:34 AM . Last Modified: 2024-04-08 04:08 AM
Hi John!
It's normal that racks are not showed in EE editor.
You should use wizard from IT Load button to configure rack's load.
(CID:110004017)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:34 AM . Last Modified: 2024-04-08 04:08 AM
Ohh... Chris was ahead of me for a minute ))
(CID:110004018)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:34 AM . Last Modified: 2024-04-08 04:08 AM
🙂
(CID:110004020)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:34 AM . Last Modified: 2023-10-22 03:43 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.