RDU alarm set point in DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • RDU alarm set point in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:37 AM . Last Modified: ‎2024-04-08 10:44 PM

0 Likes
7
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:37 AM . Last Modified: ‎2024-04-08 10:44 PM

RDU alarm set point in DCE

We have DCE 7.3.1.  There are 2 RDU in a room that is connected to DCE.  The problem right now is that we don't have enough of a load to keep the RDU's busy enough.  As a result, we are getting a "RDU:  Condensing temperature high violation exists." alarm, which clears and then returns.  How can I adjust the alarm point to reduce the alarms?  Also, can a reminder be established on the alarm set point to reset it back to default at some time in the future?

 

Thanks.

(CID:108827329)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:44 PM

0 Likes
2
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:44 PM

Hi Michael,

 

sorry i misread RDU as PDU. I'm not as familiar with the RDU but if it is a threshold, your options would be similar. You can change thresholds through the unit or similar DCE menus.   

If it is not a threshold on the device and still an alarm, you can put the device into maintenance mode so all alarms will not be sent through DCE or you can just disable the alarm. 

 

Again, sorry for the misunderstanding. 

 

Steve. 

(CID:108827353)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:37 AM . Last Modified: ‎2024-04-08 10:44 PM

0 Likes
2
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:37 AM . Last Modified: ‎2024-04-08 10:44 PM

Hi Michael,

 

There are 2 different thresholds that could be set here.You could have a manual threshold set in DCE specifically or, if you have not created one in DCE, you would have a device threshold on the PDUs themselves.

 

the way you're explaining it, I'm assuming it's on the PDU so there are again 2 ways to configure them. Since there are only 2, you could log into each device and manually change the threshold. You would go to the environmental page (this is a screenshot of a 6.x firmware)

choose configure, then edit the appropriate settings

 

 

If you want to configure the device's threshold via DCE, you would want to go to device->APC SNMP device configuration:

Choose standard device configuration settings.

Choose configure device:

Select a configuration source (I'd choose the PDU you're using):

If no configuration has been retrieved, select retrieve device settings, then next.

Now select the units you want to configure and hit next. 

Under advanced settings, look for sensor:

 

For temp, you'd set the SENSOR_TEMP_ALARM_THRESHOLD_A

Please note that here the 2 thresholds are listed as 140 and 138 while on the device it was 60 and 59. The device was set for Celsius while DCE is showing in Fahrenheit. 

 

For 2 units though, it may just be easier to do it directly on the device.

 

There is no specific reminder alarm that you can pop up.

 

Thanks,

Steve

 

(CID:108827342)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:44 PM

In response to DCIM_Support
0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:44 PM

Hi Steven,

 

Thanks for your answer, but the alarms are actually coming from an APC RDU (Refrigerant Distribution Unit)  (not a PDU), which is part of the InRow cooling system.

(CID:108828147)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:44 PM

In response to DCIM_Support
0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:44 PM

Thanks for your update Steven. I think I understand, but I'm having a problem identifying what needs to be changed to modifying the DCE alarms. Wondering if you or someone else can help me out. Thanks

(CID:108828148)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:44 PM

0 Likes
2
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:44 PM

Hi Michael,

 

sorry i misread RDU as PDU. I'm not as familiar with the RDU but if it is a threshold, your options would be similar. You can change thresholds through the unit or similar DCE menus.   

If it is not a threshold on the device and still an alarm, you can put the device into maintenance mode so all alarms will not be sent through DCE or you can just disable the alarm. 

 

Again, sorry for the misunderstanding. 

 

Steve. 

(CID:108827353)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:43 PM

In response to DCIM_Support
0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:43 PM

Hi Michael, If you need someone on the phone, you can contact technical support and if need be (and if allowed), they can remotely access your system and assist in troubleshooting of figuring out exactly what needs to be done. As for the specific issue, as I mentioned you can right click the device and put it into maintenance mode and no events at all should be sent from DCE. You can also click the alarm configuration tab, device alarm configurations, find the unit(s) in question on the left in the default layout, then find the message on the right that matches the error. You can then edit that alarm and disable it. Again, you'll have to manually re-enable it. As for the device itself, I don't have one available and not knowing the device itself, I can't specifically tell you how to reconfigure the device to reconfigure the sensor if that is possible. If there's someone else on these forums more familiar with the RDU, please feel free to assist Michael with this question. Steve.

(CID:108827403)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:43 PM

In response to DCIM_Support
0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2024-04-08 10:43 PM

Hi Steve, Thank you very much for your assistance. I think that I found the area to disable the alert that I was looking for, per your instructions. I would be nice if I could actually have adjusted the values where the alerts are triggered. As this option did not exist, I disabled the alert for now, and put a reminder in my calendar to look at this in a couple of weeks. Thanks again 🙂

(CID:108827450)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2023-10-22 03:41 AM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:38 AM . Last Modified: ‎2023-10-22 03:41 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of