Hi All
i cannot find how to configure PCBE with 25 node to discover all ups in my network.
These Ups are connected by network card
thanks
(CID:132671453)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:07 PM . Last Modified: 2024-04-04 03:56 AM
Hi Gianluca,
PowerChute Business Edition (PCBE) only communicates to UPS units connected by serial or USB connections. If you wish to monitor the UPS with a network management card, you simply browse to it. If you want shutdown based on communications with the network management card, you'll want to use PowerChute Network Shutdown or PCNS.
Thanks,
Steve
(CID:132671457)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:08 PM . Last Modified: 2024-04-04 03:56 AM
You chose DCE as the product, are you trying to add these units to DCE or are you simply trying to use the shutdown software?
(CID:132671463)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:08 PM . Last Modified: 2024-04-04 03:56 AM
hi steven
i choose DCE because otherwise i cannot post a question.
our salesman has sold a version 9.1.1 with 25 node to a customer to monitor all his UPS in a consolle
(CID:132671467)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:08 PM . Last Modified: 2024-04-04 03:56 AM
Hey Gianluca,
If it was sold from Schneider, you may want to look into helping him get his money back. If not, he should go back to his reseller. PCBE can't monitor the NMC. Sorry
Steve
(CID:132671476)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:08 PM . Last Modified: 2024-04-04 03:56 AM
Perfect.
better a DCE + PCNS
(CID:132671480)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:08 PM . Last Modified: 2023-10-22 03:37 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.