Hi Team!
I need an advice for power dependency configuration with some kind of redundancy distribution.
We have a non-standart connections from racks to power panel. We have one circuit breaker for each rack at power panel, then we have a feed to junction box, where it's splitted into two feeds. One of them feeds rack-mounted UPS with rackPDU and other feeds second rack-PDU.
You can see diagram at the picture:

In this case we have two issues:
Do you have any ideas?
(CID:96764740)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 12:42 PM . Last Modified: β2024-04-09 11:44 PM
Thank you for reporting on your power setup. It is always interesting what kind of setups our customers have.
I have one question for you - is there a 3 phase UPS somewhere in the picture? E.g. is the main power panel - that provides power to the racks protected by a 3 phase UPS?
Now on to your questions:
The good news is that we are working on supporting single phase UPS for the release coming after 7.5.
The other feature you are missing is a junction box. I'm not aware of any good ways to model that at the present moment. We do have plans for modelling "in-rack distribution panels". This could solve your problem as it would allow to create a connection from a power panel to a small "in-rack distribution panel" with two outlets.
Unfortunately I see no good workarounds. The only one I can think of is to create a small floor standing PDU. But as you mention your self it will show up on the power path.
(CID:96764971)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 12:42 PM . Last Modified: β2024-04-09 11:44 PM
Thank you for reporting on your power setup. It is always interesting what kind of setups our customers have.
I have one question for you - is there a 3 phase UPS somewhere in the picture? E.g. is the main power panel - that provides power to the racks protected by a 3 phase UPS?
Now on to your questions:
The good news is that we are working on supporting single phase UPS for the release coming after 7.5.
The other feature you are missing is a junction box. I'm not aware of any good ways to model that at the present moment. We do have plans for modelling "in-rack distribution panels". This could solve your problem as it would allow to create a connection from a power panel to a small "in-rack distribution panel" with two outlets.
Unfortunately I see no good workarounds. The only one I can think of is to create a small floor standing PDU. But as you mention your self it will show up on the power path.
(CID:96764971)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 12:43 PM . Last Modified: β2024-04-09 11:44 PM
Thank you Anders! To your question: yes, there is a 3-phase "main" UPS. Whole chain looks like this: Facility mains -> UPS -> Power panel -> Circuit breaker -> rack PDU -> load |-> rack UPS -> load In my mind, it's will be very useful to add upstream connections to the UPS models - to bigger UPS or facility switchgear.
(CID:96764983)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 12:43 PM . Last Modified: β2024-04-09 11:44 PM
I have always wondered about the setup that you describe. If an outage appears - what happens when power come back? How do you handle the Rack UPS from a capacity point of view? They do not only carry the load - but they do them self generate an extra load for charging the batteries. So the A feed carry the server load and the B feed carry the server load and the rack UPS Charging load. We are also looking into having upstream connections from UPS to switch gear etc - be a little patient it is not that far away π /Anders
(CID:96765029)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 12:43 PM . Last Modified: β2023-10-31 11:30 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.