Can we send alarm notifications for just one bullet point on this list? I like to send an email nofitication for bad input power to our maintenance department. This is for the EcoStruxureIT product.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-11 12:38 PM
Hi @trant
You can configure notifications for a single event on the device itself. See the Notifications section of this NMC user guide: https://download.schneider-electric.com/files?p_Doc_Ref=SPD_CCON-AYCEFJ_EN&p_enDocType=User+guide&p_...
Jackie
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-15 12:03 PM
Thank you for the response! Is there way to do this in EcoStruxtureIT? I like to configure 500+ UPSs for my campus enviornment.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-16 08:41 AM
Have you tried creating an alarm threshold for input power in IT Expert? Go to Alarms > Thresholds > Configure new thresholds.
Here's a help center article:
https://community.se.com/t5/Alarms/Configure-alarm-thresholds-for-notifications/ta-p/446857