Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Power Summary Data in DCO

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Power Summary Data in DCO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:06 PM . Last Modified: ‎2024-04-08 01:24 AM

0 Likes
7
1417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:06 PM . Last Modified: ‎2024-04-08 01:24 AM

Power Summary Data in DCO

On the screenshot attached I have the power summary data from an AP7853 rPDU and all the figures highlighted in blue match the figures I get from DCE. 

My questions are :- 

Why is the same information shown twice on this screenshot?

What is the relevance of the "Total power output (Avg)" and "Total output power (Peak)" values and how does DCO use them? They appear to be a sum of the "Power output (Avg)" for each bank, but since this appears to be replicated data the "Total power output (Avg)" would appear to have no relevance.  It is simply double the sum of the average power on the 2 banks of the PDU.

Can you explain please?

Thank you

(CID:114233711)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

0 Likes
3
1417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

Hi Garry,

That is a good find.

I tried to reproduce the issue (DCO 8.0) with a rack PDU in 3 device groups and - just as in you case - the property page showed a section for each device group and a 3 times total.

But the good news is, when looking at the rack PDU tool-tip the measured data was correct - so it seems that the issue is isolated to that particular property page, and the rest of the system is using the correct data.

Best Regards,

Gert

(CID:114820884)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:06 PM . Last Modified: ‎2024-04-08 01:24 AM

0 Likes
0
1417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:06 PM . Last Modified: ‎2024-04-08 01:24 AM

Hi Garry,

Do you see this duplication with all your associated AP7853 rpdu's? Would it be possible to ask for a copy of the DCO backup file and server logs (can be collected from the webmin interface)? I will send you an invite to my =S= box shortly (just in case if you would share your data safely with me), thanks.

Kind regards

(CID:114233981)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

0 Likes
0
1417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

I think I have figured it out.

 

The PDU's that show the information twice are in separate groups that are NOT in the same subtree. So for example on the attached image: -

Rack PDU1 does not DOES show replicated data
Rack PDU2 does not does NOT show replicated data
Rack PDU3 does not does NOT show replicated data
Rack PDU4 does not DOES show replicated data
Rack PDU5 does not does NOT show replicated data

Hope this makes sense

 

(CID:114234070)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

0 Likes
3
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

Hi Garry,

That is a good find.

I tried to reproduce the issue (DCO 8.0) with a rack PDU in 3 device groups and - just as in you case - the property page showed a section for each device group and a 3 times total.

But the good news is, when looking at the rack PDU tool-tip the measured data was correct - so it seems that the issue is isolated to that particular property page, and the rest of the system is using the correct data.

Best Regards,

Gert

(CID:114820884)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

In response to DCIM_Support
0 Likes
0
1417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

I noticed that the tooltip data for the rack power usage appeared to be correct, but I am still interested and a little concerned as to what the "Total power output (Avg)" and "Total output power (Peak)" values are used for.  If it is simply so that it can be displayed on the page then not such a worry, but if these values are being used for behind the scenes calculations then it may have as yet unseen knock on effects in DCO.

 

Is there any way to confirm if the data is used elsewhere?

(CID:114820894)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

In response to DCIM_Support
0 Likes
0
1417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

Hi Garry,

I will log an investigation/enhancement case for this, so it can be investigated and also verified if it has impact elsewhere. Many thanks for reporting and finding the cause.

Kind regards

(CID:114821078)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

In response to DCIM_Support
0 Likes
0
1417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2024-04-08 01:24 AM

Thanks Jef

(CID:114821082)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2023-10-22 03:36 AM

0 Likes
0
1417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:07 PM . Last Modified: ‎2023-10-22 03:36 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore