Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

PDPM138H-5U DDF - StruxureWare v7.6.0

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • PDPM138H-5U DDF - StruxureWare v7.6.0
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:56 PM . Last Modified: ‎2024-04-03 11:15 PM

0 Likes
11
1266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:56 PM . Last Modified: ‎2024-04-03 11:15 PM

PDPM138H-5U DDF - StruxureWare v7.6.0

Hello,


I'm looking for a DDF for PDPM138H-5U.  Our environment is StruxureWare v7.6.0.


Thanks!

(CID:137731447)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:56 PM . Last Modified: ‎2024-04-03 11:15 PM

0 Likes
6
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:56 PM . Last Modified: ‎2024-04-03 11:15 PM

Hi Eric,

 

Existing DDFs can be found here:

http://sxwhelpcenter.ecostruxureit.com/devices

There's also a way to request a new DDF on that page as well as an instructional video.


Thanks,

Steve

(CID:137731457)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:56 PM . Last Modified: ‎2024-04-03 11:15 PM

In response to DCIM_Support
0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:56 PM . Last Modified: ‎2024-04-03 11:15 PM

Thanks Steve.  I've searched the Device Support page for DDF files pertaining to PDPM138H-5U, but they don't have any files available.  I've put in a device request for the above model. 


Eric

(CID:140217532)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

In response to DCIM_Support
0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

It may take a little time but they should be able to get you what you need.

(CID:140217514)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

In response to DCIM_Support
0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

I was under the impression that support for this Modular PDU was provided by DDFs that are already included/shipped with DCE? Have you tried to add the device yet Eric or just planning for the future?

(CID:140217530)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

In response to DCIM_Support
0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

Thanks Steve. 

 

Angela, I was not aware the DDF was included with DCE.  I've added the device to several of our servers.  One server is giving me an alert:

 

'Device status may be inaccurate because an attempt to transfer a DDF failed.'

 

I've reviewed the DCIM/Ecostruxureit posts about this error, but cannot pinpoint why it does not alarm in 2 of my servers, but does in the 3rd server. 

 

Any assistance is greatly appreciated.


Eric

(CID:140217522)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

In response to DCIM_Support
0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

To add, what is the specific DDF that this modular PDU uses, specifically PDPM138H-5U?

 

Thanks,

Eric

(CID:140217526)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

In response to DCIM_Support
0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

Hi Eric - OK, that error message relates to the alarm (alerting) DDF. The DDFs they make under Device Support are what we call scanner DDFs and they do different things and are different files.

For the error message you have, refer to this FAQ for things to check, hopefully it is just a configuration issue with adding the device file transfer settings: http://www.apc.com/us/en/faqs/FA177004

Lastly, I think this this unit uses APC PDU. Sometimes devices may reference a few DDFs but most of the stuff should be in APC PDU.

(CID:140217518)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

Dear Eric Davis,

Tell us, please, did you solve your question or not?

With respect.

(CID:139693970)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:15 PM

Yes, the necessary DDF is included with the StruxureWare DCE v7.6.0 software.  The issue had to do with file transfer protocols. 

 

Resolution:

Enabled only FTP on device, rebooted.

Set up FTP only under 'Device File Transfer Settings'

(CID:139694225)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:14 PM

0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2024-04-03 11:14 PM

Ok, thanks for the feedback.

(CID:139694227)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2023-10-22 03:29 AM

0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:57 PM . Last Modified: ‎2023-10-22 03:29 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore