No update to DDF change request since March 13
  • No update to DDF change request since March 13
129
72
Posted: ‎2020-07-04 04:56 PM . Last Modified: ‎2024-04-05 12:05 AM
931
I made a request to add alarms to DSE7420 DDF since March. Should I send a new change request?
(CID:130099621)
Replies 6
931
Hello Yang,  I apologize that this request has not been updated since March.  Do you have a request number that you can share so that I can look into this for you?  You mentioned "DSE7420", did you mean DCE 7.4.2?  Which specific alarms and/or DDF were you looking to have changed?
Thanks.
(CID:130100093)
The device is Deep Sea DSE 7420 controller.
Here is the conversation I had with the support:
DSE7420        Supported
  •                     Please update DDF file as per the attached request form.
  • Yang Gao Tue Feb 20 15:29:07 CET 2018
  • Modbus DDF Request For DSE7420.doc
  •                     Hi, Assigned this to the concerned developer, he will get back to you as soon as possible. Regards, Moloy
  • Moloy Das Wed Feb 21 05:59:22 CET 2018
  •                     Hello, I made the requested updates and sent the new DDF for review. I will submit the DDF once its approved. Regards.
  • Ragupathy Kandasamy Thu Mar 01 14:39:16 CET 2018
  •                     Hello, The DDF for the DSE7420 is attached. Please test and let us know if there are any problems. To import: Main menu->Device->Modbus Device Communication Settings->Device Definition Files->Add/Update Definitions Note: Please quote the DDF number 2661 in future when you contact me so that I can identify the request from you Thanks, Ragupathy Kandasamy.
  • Ragupathy Kandasamy Wed Mar 14 06:49:10 CET 2018
  • dse_7420.zip
  •                     Some additional changes: - There are some sensors that display values such as 65535 (FFFF), 32767(7FFF), 4294967295(FFFFFFFF). can these values be mapped to something else?. Please see the attached device sensors snapshot - Add device alarms defined in page 154 for DSE7420. Please see the attached XML code for the alarms.
  • Yang Gao Wed Mar 14 15:34:43 CET 2018
  • DeviceSensors.pdf
  •                     Device alarms XML code
  • Yang Gao Wed Mar 14 15:35:44 CET 2018
  • dse_7420_page154_alarms.txt
  • Yang Gao Wed Mar 14 15:43:05 CET 2018
  •                     Register 1560, 1568 and 1576 should be uint32 as they use two offsets
  • Yang Gao Wed Mar 14 17:52:23 CET 2018
  •                     Correction: mains and generator total watts are 32S, main and generator total VA are 32 and mains and generator total VAr are 32S.
  • Yang Gao Wed Mar 14 18:00:03 CET 2018
  •                     Can you please make the changes as I mentioned above for alarms and some sensors?
  • Yang Gao Fri Mar 23 17:29:54 CET 2018
(CID:130100113)
Hello Yang,
Thank you for the detailed response.  I will check on this now and get back to you as soon as possible.
Thank you.
(CID:130100117)
Posted: ‎2020-07-04 04:56 PM . Last Modified: ‎2024-04-05 12:04 AM
it's been another month and there is no update.
(CID:131966280)
I would like the Modbus DDF for this hardware too... if possible...
Getting trouble with one of that Controllers
(CID:132656792)
Posted: ‎2020-07-04 04:57 PM . Last Modified: ‎2023-10-22 03:27 AM