Netbotz Trend Issues

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz Trend Issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
JSmith
Lieutenant JSmith
Lieutenant

Posted: ‎2020-05-11 07:33 AM

0 Likes
2
2350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-11 07:33 AM

Netbotz Trend Issues

I have a Netbotz 570 with several sensors, two of those happen to be recording temperature. Probe 1 is a Temp/Humidity prove and Probe 2 is a regular Temp probe. While looking at a Temperature Report Trend in DCE I get the following:

 

Probe 1 seems to be reporting values back every 30 seconds while Probe 2 seems to be reporting back all over the place sometimes there are minutes between values.There are some larger gaps in both sensors however I do get more data points in sensor 1 then sensor 2. Shouldn't I at least be seeing the same data points at the same time for both or all the senors in the Netbotz?

 

Any idea how to even start troubleshooting this or adjusting when the values get taken?

 

Regards,

 

J

 

Regards,

J
Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2020-05-20 07:03 AM

2 Likes
0
2309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-20 07:03 AM

Hi @JSmith ,

 

Unlike SNMP where DCE will poll a device for each of it's individual sensors on a regular schedule and gets a single data point in return, NetBotz are polled for their data and DCE receives back XML data that includes all the changes since the last poll. If probe 1 has not changed in 10 minutes (assuming a 5 minute polling cycle), DCE may not receive any new data about that sensor. In contrast, I can recall seeing a faulty sensor on an old NetBotz sensor pod 120 where the sensor was sending the device, and in turn device sending DCE, hundreds of values per minute. DCE.

 

In short, no, you can not configure the systems to only get a single value every 5 minutes like you can with an SNMP device, sorry.

 

If on the other hand you feel these values are in error, perhaps that's another story and maybe you need to discuss that with your local tech support. If they appear valid however and they're coming in 10 times per minute on one and once a minute on the other, that's simply the way the system operates.

 

Thanks,

Steve

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2020-05-19 07:21 AM

0 Likes
0
2319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-19 07:21 AM

Hi John,

 

Thanks for posting! I'll see if I can get some eyes on this.

 

Thanks,

Stine

Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2020-05-20 07:03 AM

2 Likes
0
2310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-20 07:03 AM

Hi @JSmith ,

 

Unlike SNMP where DCE will poll a device for each of it's individual sensors on a regular schedule and gets a single data point in return, NetBotz are polled for their data and DCE receives back XML data that includes all the changes since the last poll. If probe 1 has not changed in 10 minutes (assuming a 5 minute polling cycle), DCE may not receive any new data about that sensor. In contrast, I can recall seeing a faulty sensor on an old NetBotz sensor pod 120 where the sensor was sending the device, and in turn device sending DCE, hundreds of values per minute. DCE.

 

In short, no, you can not configure the systems to only get a single value every 5 minutes like you can with an SNMP device, sorry.

 

If on the other hand you feel these values are in error, perhaps that's another story and maybe you need to discuss that with your local tech support. If they appear valid however and they're coming in 10 times per minute on one and once a minute on the other, that's simply the way the system operates.

 

Thanks,

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore