Hi
Some of our Netbotz are appearing as (Post-only) in Data Center Expert. I can see various articles on what Post-only mode is, and how to put devices into Post-only mode, but nothing on how to take a Netbotz out of Post-only mode. Removing any Post-only settings just causes errors because it expects them. Can anyone help please?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: Thursday
Hello @Infra,
I don't have one to test with, but I believe that if you disable the post-only mode on the NB side and then run a discovery for the NetBotz appliance again in DCE (without removing the device) it may clear things up for you.
Kind Regards,
Cory
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 10 hours ago . Last Modified: 10 hours ago
You need to connect to the netbot appliance with the advanced view desktop client https://updates.apc.com/botz/av/install.htm
Once connected to the netbot, you go tools-->post only mode and you can put it in/out of post only mode
This is also covered in the netbot manual
https://iportal2.schneider-electric.com/Contents/docs/UPS-NBWL0355A_USER%20GUIDE.PDF