Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
shemil_usman
Ensign
Ensign
0 Likes
7
3871

Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi,
 
We have added two Netbotz705 (V 5.2.2.63) to DCE 7.8 and getting Critical Alert "Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed"
 
I have done the below as per software guide and K-base docs:
 
- root user name and password was added in snmp device file transfer setting
- SCP was selected with port 22
- web user name and password  was added in Netbotz Applianc credentials.
- FTP & SCP Ports are opened between DCE and Netbotz750
 
Moreover when I scan and look for device sensors I am able to see all sensors and their values.
But Critical error is still there.
 
Please advise a solution.
 
Thanks & Regards
Shemil
Attachments
Tags (1)

Accepted Solutions
shemil_usman
Ensign
Ensign
0 Likes
1
3287

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi,

 

We enabled icmp (ping command) in the firewall between Netbotz750 and DCE 7.8.0 and it worked.

 

Regards

Shemil

See Answer In Context

Tags (1)
7 Replies 7
APC_Steve
Commander Commander
Commander
0 Likes
4
3865

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi @shemil_usman ,

 

Has the appliance been reset to defaults? Initial runs of the 750s came with older firmware that when upgraded, you also needed to reset the device to defaults. If this is not done, there may be all sorts of strange issues.

 

Have you tried logging in with putty to verify the root user name and password? You might even try something like winscp to make sure you can get into the bot using scp:

 
 
 

 

 

As for seeing sensors, that's normal and not really applicable.

The DDF that DCE is trying to download has nothing to do with the sensors. The sensor DDFs are either pre-loaded on the system or manually added. They're called Scanner DDFs. The DDF that is downloaded from an APC device is used to add or update the information in the alarms page. It's called an essential alerts DDF as opposed to a scanner DDF.

 

Steve

Tags (1)
shemil_usman
Ensign
Ensign
0 Likes
0
3770

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi @APC_Steve ,

 

The Netbotz-750 came pre-configured with our Pre-fab Container Data Center with initial firmware 5.2.0. After upgrade to 5.2.26 I did not reset the device to defaults because I was afraid of getting communication lost with POD-170's (as per my previous project experience with 750 and the Access POD's) and also we have many relay connections configured from fire panels, ATS etc.

So I don't want to re-configure them because its a critical site.

 

Now what I see here is that the Netbotz750 on its own is working fine and also POD-170's and POD-150 are working well. Issue is that the DDF file is not getting transferred and failing and getting Critical alert in DCE 7.8.0.

I did log in using putty and verified the root user name and password (same is added in DCE 7.8.0)

 

I need to try the winscp and update you.  

 

Thanks & Regards

Shemil

Tags (1)
Constantin
Ensign Ensign
Ensign
0 Likes
2
3296

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi

I hope that you well?  I have a same issue with Netbotz 750 and DCE 7.8 . Did you  obtained solution for this issue?

Regards!

Tags (1)
shemil_usman
Ensign
Ensign
0 Likes
1
3288

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi,

 

We enabled icmp (ping command) in the firewall between Netbotz750 and DCE 7.8.0 and it worked.

 

Regards

Shemil

Tags (1)
Constantin
Ensign Ensign
Ensign
0 Likes
0
3282

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi 

Please share with me the procedure for activating the ICMP.

 Regards!

Tags (1)
Constantin
Ensign Ensign
Ensign
0 Likes
1
3139

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi 

It works now. Thank you for your support.

Regards!

Tags (1)
sesa157186_brid
Ensign Ensign
Ensign
0 Likes
0
2535

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi 

I also have same issue and could you share me the procedure for enable icmp from 750 to DCE ?

Thank you .