We want to cascade 4 NetBotz Sensor Pods 150 to a NetBotz Rack Monitor 250, but it is preferable in terms of A-Link cable routing to have the NetBotz Rack Monitor 250 inbetween the Sensor Pods within the system architecture, as shown in the attached sketch. Is this possible or does the NetBotz Rack Monitor 250 have to be on one end of the A-Link bus?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-11 06:26 AM
Hi @Anonymous user ,
You have 2 A-link ports on the NetBotz 250 so you can use it either way, you can have the 250 at one end and link the 4 150 pods together or you can have 2 pods on one A-link port and 2 on the other port. It's up to you.
If you are using 4 in one port, I would also consider using an external power supply (ap9505I) for supplemental power. I don't believe this would be necessary if you have 2 in one port and 2 in another.
Thanks,
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-11 06:26 AM
Hi @Anonymous user ,
You have 2 A-link ports on the NetBotz 250 so you can use it either way, you can have the 250 at one end and link the 4 150 pods together or you can have 2 pods on one A-link port and 2 on the other port. It's up to you.
If you are using 4 in one port, I would also consider using an external power supply (ap9505I) for supplemental power. I don't believe this would be necessary if you have 2 in one port and 2 in another.
Thanks,
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of