Posted: 2024-01-23 05:02 AM
As you can see below (screenshot of a NMC2 with the latest firmware), one has the option to change individually which port the SNMP Traps are supposed to be sent to.
This field is not available on all firmwares (below screenshot of a NMC3 card with an older firmware):
So, what I am trying to find out is which version of firmware introduced the field above, on both NMC2 and NMC3 cards.
Thanks
Martin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-29 08:22 AM . Last Modified: 2024-01-29 08:23 AM
HI @MartinK,
For NMC 3, the port is configurable starting in version 2.5. Here's a link to release notes.
Sorry, I haven't found that information for NMC 2.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-29 08:22 AM . Last Modified: 2024-01-29 08:23 AM
HI @MartinK,
For NMC 3, the port is configurable starting in version 2.5. Here's a link to release notes.
Sorry, I haven't found that information for NMC 2.