Hi,
I was wondering if the Netbotz 250A is able to output dry contact NO/NC alarms to another dry contact alarm panel. We are looking at getting the 250A and want to make sure that we can enable the device to send out Major/Minor alarms via the dry contact. I think this would be on part 8 as shown below.
appreciate the help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-03 11:30 PM
Hello,
on 250 you have one output relay and yo can configure it to close/open on any alarm on netbotz equipment