Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Modbus Communication issues

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Modbus Communication issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Commander Trinxs1 Commander
11
YONGHO-KIM
Lieutenant YONGHO-KIM Lieutenant
9
ciupol
Lt. Commander ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
EcoStruxure™ Hybrid DCS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Start a Topic
EngYoug006
Ensign EngYoug006
Ensign

Posted: ‎2023-05-07 02:16 AM . Last Modified: ‎2023-05-07 02:40 AM

0 Likes
4
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-07 02:16 AM . Last Modified: ‎2023-05-07 02:40 AM

Modbus Communication issues

Hi everyone,

 

We are constantly facing communication loss between Modbus Devices (TeSys, ATS48, PM8000, SEPAM...) and PLC (M580 Hotstanby) in our Ecostruxure Hybrid DCS system ,  with recurrent following alarms for instance; Device warning, Device Failure, Comm Error, ... (refer to Alaram File.pdf). Note that this issue occurs on different zones, devices stop randomly which increases plant downtime. 
We explored and checked many possibilities  (Earthing, harmonics, made some software changes on both filed and PLC side: Hybrid DCS template and DFBs;  Egx Gateways settings or eNOC port settings; hardware issues such as cables, gateways or switches... see COM Diagnostics.pdf )but still couldn't solve the problem.
 
Thank you
Attachments
COM Diagnostics.rar
Labels
  • Labels:
  • Tips and ideas
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Hennie_Smith
Lieutenant Hennie_Smith Lieutenant
Lieutenant

Posted: ‎2024-06-21 08:43 PM

0 Likes
1
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-21 08:43 PM

Have you checked the 24Vdc on the equipment including network switches? I had it in the past if the V drop just enough, I got comms errors. Measure at the end in the MCC furthest from the power supply. Are your motor starter contactors coils AC or 24Vdc since on the 24Vdc coils, the power drawn to energize these contactors are quite high.

Reply

Link copied. Please paste this link to share this article on your social media post.

EngYoug06
Crewman EngYoug06
Crewman

Posted: ‎2024-06-22 09:11 PM

In response to Hennie_Smith
0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-22 09:11 PM

We checked everything and issues don't come from the 24Vdc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Siddiqui
Ensign Siddiqui Ensign
Ensign

Posted: ‎2024-06-25 12:22 AM

0 Likes
1
1607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-25 12:22 AM

I am not an expert on hybrid DCS, but I can provide the following comments on the network side.

 

Can you please check the network status? Ensure the network is stable and there is no storm inside the network.

 

Additionally, you can capture the packets and perform the Wireshark analysis to get more insight into details.

 

From the shared snapshot of the eNOC messaging, I can see there are errors.

 

From the M580 point of view, the BMENOC module scans all the devices. So, you can configure Port 1 (Service Port) of the BMENOC0301/X module as a Mirror port and capture the packets.

 

The capture provides details on what is going on at that network level. You can also track down the analysis at the device level. Which devices are not responding to the requests? Or is the scanning rate much faster than the device's response capability?

 

Wireshark analysis requires expertise. If you can do it, it's good. Otherwise, please create a ticket with the support team providing all the investigation details.

 

I hope the above comments provide help.                                                          

Reply

Link copied. Please paste this link to share this article on your social media post.

EngYoug06
Crewman EngYoug06
Crewman

Posted: ‎2024-06-25 08:17 PM . Last Modified: ‎2024-06-26 07:44 AM

In response to Siddiqui
1 Like
0
1577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-25 08:17 PM . Last Modified: ‎2024-06-26 07:44 AM

@Siddiqui Thank you so much for your help. We performed all of the described checkings as well as the creation of a ticket. After having tried most of recommendations we decided to replace gateways by M241 PLC and it seems to have brought enhancements and considerably decreased errors.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore