Missing values in DCO

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
8
351

Missing values in DCO

This question was originally posted on DCIM Support by Boris Majdandzic on 2018-10-25


Hi, I have problem with values from UPS in DCO. I can`t see amps on phase one of the UPS devices from DCE. In DCE I can see all values.

I have already asked this in the theme:

But I was told to wait for 30 days & it would solve it self. But still the same.

Please help.

(CID:134689513)

8 Replies 8
DCIM_Support
Picard
Picard
0 Likes
0
351

Re: Missing values in DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-10-30


Is anybody answering anything at all?

(CID:134691623)

DCIM_Support
Picard
Picard
0 Likes
0
351

Re: Missing values in DCO

This comment was originally posted on DCIM Support by Jef Faridi on 2018-10-30


Hi Boris,

What is the version of your DCO and DCE?

I'm currently running some tests - will get back to you as soon as possible.

Kind regards

(CID:134691713)

DCIM_Support
Picard
Picard
0 Likes
0
351

Re: Missing values in DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-10-30


Hi Jef,

DCE 7.5.0. & DCO 8.2.7

(CID:134691756)

DCIM_Support
Picard
Picard
0 Likes
3
351

Re: Missing values in DCO

This answer was originally posted on DCIM Support by Jef Faridi on 2018-11-09


Hi Boris,

I was able to reproduce a similar issue with another UPS unit (Symmetra 160K) - issue basically DDF related, where the device output current sensors are not being correctly reported to DCO. 

Can you send a walk of your UPS device (I guess that's a Legrand Archimod HE device, right?)

Instructions for performing a walk file available here:   

How to create a SNMP walk file for Struxureware Data Center Expert/EcoStruxure IT Gateway

Thanks,

Kind regards

(CID:134695529)

DCIM_Support
Picard
Picard
0 Likes
0
351

Re: Missing values in DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-12


Archimod.walk

Hi, here is the walk file.

(CID:134696228)

DCIM_Support
Picard
Picard
0 Likes
0
351

Re: Missing values in DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-20


Hi Jeff, 

 

Did you recive walk? is there any news?

(CID:136153915)

DCIM_Support
Picard
Picard
0 Likes
0
351

Re: Missing values in DCO

This comment was originally posted on DCIM Support by Jef Faridi on 2018-11-22


Hi Boris,

Yes, thanks I have the walk file - appears to be ddf related (new ddf can be requested from Device support

 http://sxwhelpcenter.ecostruxureit.com/devices)

This is also reported to DCE/DDF development team for possible enhancements in a future version.