I have EcoStructure Data Center Expert and want to migrate it to a different host (not within the same cluster). What is the best way to do this?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-05 05:39 PM
Hello @ocappsjr,
I recommend before taking any actions that you take a backup of the Data Center Expert appliance from within the Desktop Client under the System menu > Server Administration Settings > Server Backup/Restore.
Once you have a backup, the VM should be able to be migrated to a new host as long as the MAC address remains the same.
If you have issues with this, then you would need to deploy a new VM that is running the same version as your old VM using the same amount of resources and then restore a backup to it. If the MAC address changes, licensing would need to be migrated to the new system by technical support.
Kind Regards,
Cory