Hi Team!
I'm testing Manual Power measurements import feature now.
I have several power panels feeded by main power panel with power measuring devices in my setup.
I want to use manual power measurements feature for panel load visualization.
I've create excel spreadsheet and upload it to DCO.
Now I have measured load on Main panels, but it not reflects on connected power consumers.
Main panel:
Connected "child":
In the same time, if I connect rPDU to Main panel, imported measured load will be transfered to rPDu level and displayed on the tooltip:
I assume it happens because of different consumer types, so the question:
How can I display measured power on "child" power panels if I have measures from Main panel breakers?
Do we have any options to "link" measured values to input breaker of power panel for example?
(CID:143760788)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:34 PM . Last Modified: 2024-04-03 02:36 AM
Hello Valentin. I assume the measurements you have displayed above represent the totals for the pdu but you also have breaker level power values?
If yes, then you have to look at sensor mapping the breaker sensors to the breaker poles in the panels inside the pdu's. Once the breaker sensors are mapped to the breaker poles, you should see power data downstream on your rack pdu's and so on.
https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Configuring+branch+circuit+monitoring
Keep in mind the power overlay on racks and rack pdu's displays power data in watts/Kw not amps so you will want to map your watts/Kw power data if you have that.
Regards
Greg Sterling
(CID:143760914)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:34 PM . Last Modified: 2024-04-03 02:36 AM
Hi Greg!
I use buit-in transformation according to this article: https://sxwhelpcenter.ecostruxureit.com/display/public/UADCO8x/Importing+manual+power+measurements
So, I fill excel template with values and import it to DCO. It was automatically associated with objects in model and I have measures on breaker level:
In this example I connect power panel (which represent busbar section in my model) to breaker in positions 1-2-3 and rPDU to breaker in positions 4-5-6/
The problem is that measures are not displayed downstream on connected power panel. It's displays fine on rPDU and rack, but not on power panel.
Am I miss something?
(CID:144311016)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:34 PM . Last Modified: 2024-04-03 02:36 AM
No, I think you are correct in that case. The downstream power should be visible on rack pdu's but I do not think it will display on downstream power devices.
Regards
Greg Sterling
(CID:144867763)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:35 PM . Last Modified: 2023-10-22 03:00 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.