MIB walk Eaton BladeUPs

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • MIB walk Eaton BladeUPs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:46 PM . Last Modified: ‎2024-04-04 11:07 PM

0 Likes
15
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:46 PM . Last Modified: ‎2024-04-04 11:07 PM

MIB walk Eaton BladeUPs

Asking on behalf of Will:

I am trying to do a mib walk of our Eaton BladeUPs so it can be imported into our DCE. However, I am getting an error about the device not responding after the mib walk is complete. Any ideas or suggestions on what it could be?

Thanks

 

(CID:132660171)

Labels
  • Labels:
  • Data Center Expert
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 15
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:46 PM . Last Modified: ‎2024-04-04 11:07 PM

0 Likes
1
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:46 PM . Last Modified: ‎2024-04-04 11:07 PM

Hi Stine, Will,

I'd start out with normal SNMP troubleshooting.. K-base FA226273 goes through a lot of things to check. The first thing I'd try is simply validating the community strings and trying from another computer.


Steve

(CID:132660189)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:46 PM . Last Modified: ‎2024-04-04 11:07 PM

In response to DCIM_Support
0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:46 PM . Last Modified: ‎2024-04-04 11:07 PM

Apologies, I missed the part where it said it was complete.  

(CID:132660398)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:07 PM

0 Likes
7
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:07 PM

Sounds like a misbehaving SNMP agent.   Is UPS at latest firmware?   Did u get the last expected OID just before error or is the walk incomplete?    An error at end of walk happens sometimes.    Question is, will DCE by affected?

(CID:132660383)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:07 PM

In response to DCIM_Support
0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:07 PM

I updated UPS to latest firmware today, thinking that was the issue but I don't get an OID.  I'm guessing walk is incomplete..

(CID:132660386)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

In response to DCIM_Support
0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

Sorry, I missed the part where it was said it completed. Have you tried a different utility to run the walk to make sure it’s not the utility at fault? 

(CID:132660399)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

In response to DCIM_Support
0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

Will,

The SNMP agent on every device, APC, Eaton et al must be well behaved.  Sadly its not always the case.  Although the presence of an error at the end of a walk does not always mean a problem - depends on the error.  Will you post your snmpwalk command and the output?

At best, you will have all the info but the agent is poorly coded.  At worst, the walk is bombing part way through.  You and/or Eaton can ascertain which it is.   If its bombing then Eaton should fix it. 

What happens when you attempt to discover the UPS in DCE?  Is it being discovered?  Is it recognised as Eaton? as a UPS? 

In the snmpwalk output do you see sysobjid, sysname, syslocation etc?  If its getting to the end of the walk then you could try submitting what you have via the usual request DDF for DCE channel.

(CID:132660433)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

In response to DCIM_Support
0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

When attempting to discover the device in DCE, nothing happens.  When I go to add device I select SNMPv1 as the discovery type, put in the ip address of the UPS, our community string, the device group, check the box for run discovery now, click finish and nothing.  If I try with modbus tcp as device type and that route, the device is discovered but it says communication has been lost.  

Here is the walk output:

#sapwalk: ver 2.7
#Copyright (c) 1994-2006 SIMPLESOFT Inc.
#Address=10.1.224.4, StartOid=1.3
#TimeOut=90000, MaxRetries=3, CompareFlag=1, DebugFlag=0
#Error: Device not responding

 

I'm missing something somewhere, just now sure what.  I tried updating the DCE is latest client was well but our service contract expired and has to be renewed but I don't think that would have anything to do with this?

(CID:132661565)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

In response to DCIM_Support
0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

Hi Will,

So it's not responding at all. Have you tried any other SNMP utilities and tried polling using the same community names from the same network segment as DCE? Maybe also try on the same network segment as the device too as it is possibly a network issue. I'll suggest again that you look into the troubleshooting doc I initially posted:

 K-base  FA226273

Steve

(CID:132661598)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

In response to DCIM_Support
0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

Can you ping the IP?

(CID:132661752)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

In response to DCIM_Support
0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:47 PM . Last Modified: ‎2024-04-04 11:06 PM

Yes I can ping the ip address

(CID:132662703)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:48 PM . Last Modified: ‎2024-04-04 11:06 PM

0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:48 PM . Last Modified: ‎2024-04-04 11:06 PM

Dear Will Jackson,

Tell us, please, could you solve your problem or not?

With respect.

(CID:132662537)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:48 PM . Last Modified: ‎2024-04-04 11:06 PM

0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:48 PM . Last Modified: ‎2024-04-04 11:06 PM

No, I have not been able to resolve this issue yet.  We are on summer hours since we are k-12 and normally have fridays

(CID:132662701)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:48 PM . Last Modified: ‎2024-04-04 11:06 PM

0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:48 PM . Last Modified: ‎2024-04-04 11:06 PM

Dear Will Jackson,

I assume that you are using a PC running MS Windows. If this is the case, then go to the web-page https://support.microsoft.com/en-us/help/310099/description-of-the-portqry-exe-command-line-utility and download either Portqry.exe or PortQueryUI tool for MS Windows.

Then perform a simple test of your UPS for listening UDP port 161 (SNMP service) as in the screenshot below:

If it's okay, you should see something like this UDP port 161 is LISTENING.

Any other result will mean either the network isolation of your UPS, or the disabled SNMP service in your UPS. In the first case, you should contact your network team for the solution of the network access problem, and in the second case - to the technical support service of your UPS.

I hope this helps you and will speed up the solution of your problem.

With respect.

(CID:132662745)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:48 PM . Last Modified: ‎2024-04-04 11:06 PM

0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:48 PM . Last Modified: ‎2024-04-04 11:06 PM

Dear Will Jackson,

Tell us, please, did you solve your problem or not?

With respect.

(CID:132670135)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:48 PM . Last Modified: ‎2023-10-22 02:59 AM

0 Likes
0
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:48 PM . Last Modified: ‎2023-10-22 02:59 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of