I need to install 12 AP9520TH, through 01 NBRK0250
Could you please tell me if that is feasible?
If so, what accessories are required for this?
(CID:143760544)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:31 PM . Last Modified: 2024-04-03 02:37 AM
Hi Javier,
Good day!
The maximum number of AP9520TH that can be added to the Netbotz 250 is eight (8).
These sensors are cascaded using Cat5 cables through the A-link ports with terminators on both ends of the line (A-link IN of the Netbotz 250 and A-link out of the 8th AP9520TH) to avoid communication loss.
To know more about this, please refer to page 10 of the Netbotz Rack Monitor 250 Installation and Configuration Guide from the Documentation section of this website.
I hope this helps.
Regards,
Justine
(CID:143760730)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:31 PM . Last Modified: 2024-04-03 02:37 AM
Hi Javier,
Good day!
The maximum number of AP9520TH that can be added to the Netbotz 250 is eight (8).
These sensors are cascaded using Cat5 cables through the A-link ports with terminators on both ends of the line (A-link IN of the Netbotz 250 and A-link out of the 8th AP9520TH) to avoid communication loss.
To know more about this, please refer to page 10 of the Netbotz Rack Monitor 250 Installation and Configuration Guide from the Documentation section of this website.
I hope this helps.
Regards,
Justine
(CID:143760730)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:31 PM . Last Modified: 2024-04-03 02:37 AM
Thanks Justine
(CID:144310769)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:31 PM . Last Modified: 2024-04-03 02:37 AM
You're welcome
(CID:144310857)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:32 PM . Last Modified: 2023-10-22 02:46 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.