Incorrect values

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Incorrect values
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:30 PM . Last Modified: ‎2024-04-05 12:12 AM

0 Likes
8
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:30 PM . Last Modified: ‎2024-04-05 12:12 AM

Incorrect values

Hi.

There are some incorrect  values displayed from the device, the first is an UPS, the sensors are unavailable but in the client show very high values.

 

the second are some ATS ASCO that display incorrect values in the client.

 

Regards.

(CID:130094976)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

0 Likes
4
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

Dear Ernesto González,

How long have you had this problem?

Did such incorrect values always exist or did they appear after some actions?

Where did you get the DDF-files for your equipment? If from the web-page Device Support, then I recommend you to do make the corresponding Request modification as it is visible on my screenshots:

And...

In any case, you can find your equipment on the above web-page and click the I WANT IT TOO button. And within one or two business days you will be sent a web-link with an instruction to download the required DDF-file. Try it.

I hope this helps you.

With respect.

(CID:130096043)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

Dear Ernesto González,

Please clarify the vendor/model of the problem UPS and ATS, as well as the versions of the DDF-files in your DCE software (what version of the DCE software?), which are used in this case.

The more you provide information, the faster you will be helped 😀.

With respect.

(CID:130095076)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

Hello.

  • The model for the UPS is Liebert eXM 100kVA, the versión of the DDF is "liebert exmups V.1"
  • The model of the ATS is of the series 300, the ATS provides the measured using  the Digital Power Meter 5210 with the controller type G, the version of the DDF is  "ASCO G5 Group Controller V.3"
  • The versión of the DCE is 7.4.1.5.

Regards.

(CID:130095858)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

0 Likes
4
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

Dear Ernesto González,

How long have you had this problem?

Did such incorrect values always exist or did they appear after some actions?

Where did you get the DDF-files for your equipment? If from the web-page Device Support, then I recommend you to do make the corresponding Request modification as it is visible on my screenshots:

And...

In any case, you can find your equipment on the above web-page and click the I WANT IT TOO button. And within one or two business days you will be sent a web-link with an instruction to download the required DDF-file. Try it.

I hope this helps you.

With respect.

(CID:130096043)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

In response to DCIM_Support
0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

Hi.
problems with the UPS only appear when the sensors turn off, they immediately show high values.
With the ATS, I requested the modifications of the DDF

Thanks for the support

(CID:130097825)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

In response to DCIM_Support
0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

Dear Ernesto González,

Indeed, because the value of 59012.6F = 32767C. A value of 32767 generally means no sensor connected.

In any case, thank you for the feedback 😀.

With respect.

(CID:130097842)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

In response to DCIM_Support
0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

Any way that this does not happen ?, I would like that when the sensor is not active it will show a zero value

 

Thanks

best regards

(CID:130098562)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

In response to DCIM_Support
0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2024-04-05 12:12 AM

Dear Ernesto González,

I would like that when the sensor is not active it will show a zero value

The fact is that it is correct to say "the sensor is connected or disconnected".

If the sensor is physically connected, it is powered and it is working, it shows some real value, for example, even 0C (this should also be normal).

If the sensor physically disconnected, no powered, or it is defective, the DCE-server displays the maximum possible integer number, which is 32767.

Why this happens in you, it is necessary to find out specifically with your UPS, and to check the normal working of its sensors and components.

With respect.

(CID:130098684)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2023-10-22 02:44 AM

0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:31 PM . Last Modified: ‎2023-10-22 02:44 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of