Hi, I have Incorrect measured values, the meter is not connected to TC's or something else but in the DCE client displays high measured values.
best regards!
(CID:130091967)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:10 PM . Last Modified: 2024-04-05 12:18 AM
Dear Ernesto González,
Perhaps you have an incorrect version of the Modbus DDF-file for your ION7650. Tell us please, what is your version of DCE software and what is the version of the Modbus DDF-file for PowerLogic ION 7650? For example, I have the latest DCE-7.5 software and the version powerlogic_ion7650.xml is v.2.
In addition, on the Device Support resource you can also find the ION7650 device as on my screenshot:
Try to press the button I WANT IT TOO and within one or two business days you will be sent a web-link to download the corresponding DDF-file. Import it into your DCE software and try. Maybe this will lead to a positive result.
If, however, you do not succeed, then you need to click on the Request modification web-link as in the screenshot above. As a result, you will make a modification request, i.e. to modify the DDF-file to ensure, that the readings of the sensors in the DCE software are correct.
I hope this helps you 😀.
With respect.
(CID:130092083)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:10 PM . Last Modified: 2024-04-05 12:18 AM
Hi, I have the version 2, does exist a new version?
(CID:130094804)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:11 PM . Last Modified: 2024-04-05 12:18 AM
Dear Ernesto González,
As soon as I have more information, I'll let you know.
With respect.
(CID:130094884)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:11 PM . Last Modified: 2024-04-05 12:18 AM
Hi Ernesto,
It looks like the raw values being returned by your ION7650 are all value 0xFFFF, which is showing up as 65535 for unsigned values and -1 for signed values, scaled as appropriate to the sensor.
It's common for Modbus devices to use the value -1 as a "Not Available" flag.
You should check to make sure your ION7650 is properly configured.
Regards,
Glenn Martin
(CID:130092301)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:11 PM . Last Modified: 2024-04-05 12:18 AM
Hi Martin.
could you help me with the configuration, I’ve download the configuration meter.
Regards.
(CID:130094918)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:11 PM . Last Modified: 2023-10-22 02:43 AM