In version 7.3.6 of DCO are not available PDU 220V 50Hz. Will fix this in version 7.4? Or is there any way to add them?
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-0208:42 AM. Last Modified: 2024-04-1001:25 AM
Good question - the Generic PDU is a floor standing Power Distribution Unit which is a 3 phase device. This implies that the voltage you set on this unit is a three phase voltage - in your case you should set the voltage to 380V 50 Hz. This will allow you to be able to connect e.g. a single phase rack mount PDU with a voltage of 220v to the Generic PDU.