ITO Discovery Problem

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • ITO Discovery Problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:12 AM . Last Modified: ‎2024-04-08 04:16 AM

0 Likes
4
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:12 AM . Last Modified: ‎2024-04-08 04:16 AM

ITO Discovery Problem

HI

I am trying to discover SNMP devices from ITO server, it starts searching but after 100% completion it showing me 0(zero) Visits and 0(zero) discovery of devices. Can you please help me to resolve this issue?

secondly can i discover SAN devices?

BR

John

 

(CID:108829445)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:12 AM . Last Modified: ‎2024-04-08 04:16 AM

0 Likes
2
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:12 AM . Last Modified: ‎2024-04-08 04:16 AM

Hello John. 

ITO is geared specifically to discover servers, blade chassis and blades.

Server discovery is expected to be very detailed in nature so that ITO can also attempt to match the server hardware to a power profile.  If your server is not running an advanced SNMP agent from the manufacturer (like HP, Dell, or IBM) then attempts to discover servers will likely not succeed as the details returned to ITO from generic SNMP agents do not provide enough specific information to allow this process to complete. 

I would advise you consider using WMI or SSH to discover windows or linux based servers, use the VMware option for VMware hosts.

SNMP is more generally geared for discovery of blade chassis, specifically HP, Dell and IBM blade chassis. SNMP is also used for polling of cpu utilization of linux and unix hosts.

Discovery of other device types like network switches and storage systems is on our product roadmap.

 

Regards

 

Greg Sterling

(CID:108829456)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:13 AM . Last Modified: ‎2024-04-08 04:16 AM

In response to DCIM_Support
0 Likes
0
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:13 AM . Last Modified: ‎2024-04-08 04:16 AM

Hello i have attached snapshot for the discovery. server visited more than devices and found the attached result. can you please tell why it is showing like this? and how to resolve this issue? BR John

ITO Discovery.PNG

(CID:109446896)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:13 AM . Last Modified: ‎2024-04-08 04:15 AM

In response to DCIM_Support
0 Likes
0
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:13 AM . Last Modified: ‎2024-04-08 04:15 AM

Hello John Just reconfirming, these are servers you're trying to discover? Based on your log entries here's some feedback. The "Unable to connect" usually means one of the following: 1. The asset is not running an SNMP agent 2. The community string specified in the discovery is incorrect 3. SNMP connection is blocked (ie. by a firewall or some other item) The "successfully connections. Unable to determine device vendor" messages mean ITO was able to connect to the SNMP agent using the community string but insufficient details to complete a detailed discovery was returned. As mentioned in the initial response.. I would advise using WMI, SSH or VMware protocols to discover servers, IPMI for discovery of management cards (like iDRAC's, ILO's and IMM cards). In most cases, SNMP will not work for discovery of servers... the only times it may work is if the server is running an advanced SNMP agent provided from the server vendor ... but for windows servers you'll still need WMI to poll the server for CPU utilized, at that point you should just use WMI. Regards Greg Sterling

(CID:109446927)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:13 AM . Last Modified: ‎2023-10-22 02:41 AM

0 Likes
0
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:13 AM . Last Modified: ‎2023-10-22 02:41 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore