Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

I’m searching firmware for Galaxy WM UPS AP9635

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • I’m searching firmware for Galaxy WM UPS AP9635
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:22 PM

0 Likes
5
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:22 PM

I’m searching firmware for Galaxy WM UPS AP9635

I could not find firmware for a Galaxy WM UPS management card AP9635.

The usual download space for web card firmware seems to be abandoned.

http://www.apc.com/au/en/tools/download/

The question is that, where can I get firmware for this webcard to this kind of UPS?

 

(CID:132653294)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:21 PM

0 Likes
3
910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:21 PM

Hi Gabor - for this UPS type, we don't post the Network Management Card - NMC (or UPS) firmware as it typically is updated by a field service engineer along with the UPS. There is often a dependency on the NMC firmware and UPS firmware for this model so it is not done independently or without recommendation.

If you think you need a firmware update, I'd suggest engaging your local technical support office to see if there is one available and/or if field service can be dispatched.

(CID:132653316)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:21 PM

0 Likes
3
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:21 PM

Hi Gabor - for this UPS type, we don't post the Network Management Card - NMC (or UPS) firmware as it typically is updated by a field service engineer along with the UPS. There is often a dependency on the NMC firmware and UPS firmware for this model so it is not done independently or without recommendation.

If you think you need a firmware update, I'd suggest engaging your local technical support office to see if there is one available and/or if field service can be dispatched.

(CID:132653316)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:21 PM

In response to DCIM_Support
0 Likes
0
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:21 PM

Hi Angela,

 

Thanks for the response. The problem is that, that we tried to get the firmware from the technical support, but they couldn’t send us the file, for some reason. They tried to send it with zip compression, but they have difficulty to send us the file. 

My college has set up the system and he needs to install this card in to the ups at the weekend. The UPS tuner doesn’t help us with the Web card firmware. (It's just for the ups system) 

In the future Schneider doesn’t support the download of this kind of management card firmware from the official website?

Where can we get this firmware file? Just from the technical support team?

(CID:132653325)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:21 PM

In response to DCIM_Support
0 Likes
0
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:21 PM

We have the solution. 😀 

 

(CID:132653334)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:21 PM

In response to DCIM_Support
0 Likes
0
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:01 PM . Last Modified: ‎2024-04-04 11:21 PM

Hi Gabor, glad if you figured out the solution.

And I understand UPS Tuner is just for UPS but if we post firmware on the website for ALL customers, I imagine there are some who will accidentally load incorrect or unsupported versions for their configuration or setup.

As you may already know, we do provide firmware downloads for the network management card on products where this is not as much of a concern but out of an abundance of caution, I think Galaxy VM/VX product owners prefer not to share NMC firmwares publicly without verification of support or field service teams first.

I understand in your scenario, needing the firmware is a valid situation and I imagine support had to verify first which NMC firmware would work with the UPS firmware on your Galaxy system. I don't think there is any easy way to force/verify that on the website with standalone downloads ☹️  Where possible though, the mantra is that we make the firmware downloadable and available to users without needing to contact any Schneider personnel.

(CID:132653339)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:02 PM . Last Modified: ‎2023-10-22 02:38 AM

0 Likes
0
910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:02 PM . Last Modified: ‎2023-10-22 02:38 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore