I Need OID of PDPM !!!
  • I Need OID of PDPM !!!
129
112
72
Posted: ‎2020-07-03 05:20 PM . Last Modified: ‎2024-04-08 12:14 AM
1836
Hello
I need OID of PDPM which model numbers are:
  • PDPM277H
  • PDPM138H-5U
The important parameters which I need in OID are:
  • Voltage
  • Currency
  • Power
  • Power Factor
  • All above parameters for each PHASE
  • All above parameters for each MODULE which is inside of PDPM,separately
I need to mention that the last MIB file that downloaded is powernet4.2.1.mib
(CID:122093901)
Posted: ‎2020-07-03 05:21 PM . Last Modified: ‎2024-04-08 12:14 AM
1836
Hi matthew.nq,
The SNMP OID that you are interested in is exactly the same for both the PDPM277H and the PDPM138H-5U, which is also part of, for example the UPS Symmetra PX All-In-One 48kW (SY48K48H-PD). And, much of the information on this question has already been published here in the topic  (read my comments there).
Thus, for all three of the above devices, we have:
"System Output Frequency - *0.1Hz:"
.1.3.6.1.4.1.318.1.1.22.4.1.4.0
"System Output Voltages Phase to Neutral - *0.1V:"
.1.3.6.1.4.1.318.1.1.22.4.1.15.1.3.(1-3)
"System Output Voltages Phase to Phase - *0.1V:"
.1.3.6.1.4.1.318.1.1.22.4.1.15.1.4.(1-3)
"System Output Current per Phases - *0.1A:"
.1.3.6.1.4.1.318.1.1.22.4.2.11.1.3.(1-3)
"System Output Power per Phases - *0.1kW:"
.1.3.6.1.4.1.318.1.1.22.4.3.5.1.2.(1-3)
"Total System Output Power - *0.1kW:"
.1.3.6.1.4.1.318.1.1.22.4.3.1.0
"Breakers Output Current per Phases (1-3) and per Modules if installed (1-24 for PDPM277H and 1-6 for PDPM138H-5U and SY48K48H-PD) - *0.1A:"
.1.3.6.1.4.1.318.1.1.22.2.4.1.9.(1-24).(1-3)
"Breakers Output Power per Phases (1-3) and per Modules if installed (1-24 for PDPM277H and 1-6 for PDPM138H-5U and SY48K48H-PD) - *0.1kW:"
.1.3.6.1.4.1.318.1.1.22.2.4.1.11.(1-24).(1-3)
"Modules Output Power (3ph mod - summ, 1-ph mod - per lines), (1-24 for PDPM277H and 1-6 for PDPM138H-5U and SY48K48H-PD) - *0.1kW:"
.1.3.6.1.4.1.318.1.1.22.2.6.1.20.(1-24).1 -- for 3ph module (PDM 3 Pole 5 Wire 16A IEC309) only one summ value present
.1.3.6.1.4.1.318.1.1.22.2.6.1.20.(1-24).(1-3) -- for 1ph module (3x1 Pole 3 Wire 3xIEC309) present all three values separate
"Modules Output Energy Usage (3ph mod - summ, 1-ph mod - per lines), (1-24 for PDPM277H and 1-6 for PDPM138H-5U and SY48K48H-PD) - *0.1kW*hour:"
.1.3.6.1.4.1.318.1.1.22.2.6.1.21.(1-24).1 -- for 3ph module (PDM 3 Pole 5 Wire 16A IEC309) only one summ value present
.1.3.6.1.4.1.318.1.1.22.2.6.1.21.(1-24).(1-3) -- for 1ph module (3x1 Pole 3 Wire 3xIEC309) present all three values separate
With best regards.
P.S.: Power factor SNMP OID for this devices does not exist.
(CID:122096422)
Replies 9
1836
Dear Matthew,
You can use freeware softwares like SNMP MIB browser to do the SNMP walk for your device and get any parameters OIDs.
Step 1: Download the SNMP MIB Browser from the below link:
http://ireasoning.com/download/mibpro/setup.exe
Step 2: Install the MIB Browser
Step 3: Launch the MIB Browser and Load MIB File of device
Step 4: Once the MIB file is loaded, please type the IP Address of the device and Click on Advance option, and type the details such as community string name: public as shown below in the screen shot.
Read Community: Public or type the community string of the device
And then click on Ok
Step 5: You can then navigate to the tree as shown below for the device to find the specific OIDs.
I hope this helps.
Bala
(CID:122093951)
Dear Bala
Your answer was helpful,thanks for your reply.
But there is an other question,I want to have specific OID's that mentioned below:
  • Voltage
  • Currency
  • Power
  • Power Factor
for these two PDPM models
  • PDPM277H
  • PDPM138H-5U
By searching in the Google i find a file which depends on PDPM277H OID's.
But couldnt find any OID's for PDPM138H-5U.
(CID:122095975)
Dear Matthew,
It is very easy to get the SNMP OIDs if you can do the SNMP walk by using the MIB browser to any SNMP device. I am sorry that I do not have an access to PDPM138H-5U, and therefore I am unable to get you the OIDs.
If possible, can you follow my instructions and do the SNMP walk to get the required SNMP OIDs of this PDPM?
You can get the specific OIDs when you select the tree of SNMP OIDs.
regards,
Bala
(CID:122096369)
Dear Balaraman
I want to thank you for your informative and quick answers.
Below of my comment , Spezialist replied an answer which can help every one who want to uses OID of these types of devices.
By the way,Thanks million million times.
(CID:122685429)
1837
Hi matthew.nq,
With best regards.
(CID:122096422)
Dear Spezialist
Thank you for your reply
I saw your comment on that topic after i post this topic.
I would test these new OID and will tell you the result of test.
with the best regards
Matthew
(CID:122685431)
Hi matthew.nq,
Thanks for the feedback: I was glad to help and answer the questions 😀.
(CID:122685439)
Your welcome man
I have one more question which is about InRow (RP & RC) series and i'm writing that topic just right now.
I wish you could help me on that issue,its so complex.
(CID:122685443)
Posted: ‎2020-07-03 05:21 PM . Last Modified: ‎2023-10-22 02:36 AM