Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

How to view alarms from PME in DCO and version compatibility

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How to view alarms from PME in DCO and version compatibility
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Jef
Captain Jef Captain
76
APC_Steve
Commander APC_Steve Commander
54
gsterling
Commander gsterling Commander
49
Cory_McDonald
Lt. Commander Cory_McDonald Lt. Commander
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 PM

0 Likes
3
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-04 03:23 PM

How to view alarms from PME in DCO and version compatibility

This question was originally posted on DCIM Support by Justen.Dimaio on 2018-03-15


Hello,

 I have a customer who would like to use both DCO and PME, specifically using DCO to view device sensors and alarms for devices in PME. I understand how to set up the integration using this link:

http://sxwhelpcenter.ecostruxureit.com/display/public/UAOp74/Configuring+StruxureWare+Power+Monitori...

But this does not specify what information will be brought into DCO.  Am I correct in assuming that once the ETL and External systems are configured, I will be able to associate the devices in PME just as I would if I added DCE as an external system as stated here?

Viewing Alarms From External Systems

I will also need to know what versions of PME are supported for this integration assuming we will be using the latest version of DCO which is currently at 8.2.2.

 

I am also going to need some insight as to how the integration will be affected if we were to use Ecostruxure IT Advisor as the aggregation point once it is released.

Please let me know if you need clarification on any of these questions.

Thank you,

 

(CID:129407729)

Labels
  • Labels:
  • Data Center Operation
  • power monitoring expert
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-04 03:23 PM

This answer was originally posted on DCIM Support by Jonathan Gould on 2018-03-16


I have used the PME to DCO integration and as far as I am aware it was mainly designed for the sharing of power readings and not alarms.   You are correct in that once it is configured on both sides (DCO and PME) then you will see the KW power values as unassigned devices in device association. 

I think the best/easiest way to get similar alarms is to have DCE read the same meters and create the alarms.  I know PME also offers OPC as a method of integration but unsure if PME exposes alarms through that interface, but if they do then it might be possible to do OPC - ETL.    

(CID:129407760)

See Answer In Context

Reply
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-04 03:23 PM

This comment was originally posted on DCIM Support by Ed Tarento on 2018-03-16


Hi Justin, I'm very interested in this topic as well but I haven't yet done the PME alarms to DCO part.  During my quick scan of the PME DCO integration page, I didn't see if PME alarms were included?

 

If not, you can bring external alarms into DCO via ETL Import Database and the "Alarm" table.  I've done that before but there were some important things to consider - assuming the PME DCO integration excludes alarms.  DCO is not designed as an alarm management tool.  Customer expectation around performance should play a big part in deciding to do this.  It can be several minutes before an alarm generated in PME appears in DCO.  To have the PME originating alarm "linked" to the DCO device requires, as I recall, to know the ci_id of the DCO device.  So some coding is required.  

Please let me know if the DCO PME integration includes PME alarms.  Can't (yet) help on IT Advisor

I hope that helps

Ed

(CID:129407748)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 PM

0 Likes
0
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-04 03:23 PM

This answer was originally posted on DCIM Support by Jonathan Gould on 2018-03-16


I have used the PME to DCO integration and as far as I am aware it was mainly designed for the sharing of power readings and not alarms.   You are correct in that once it is configured on both sides (DCO and PME) then you will see the KW power values as unassigned devices in device association. 

I think the best/easiest way to get similar alarms is to have DCE read the same meters and create the alarms.  I know PME also offers OPC as a method of integration but unsure if PME exposes alarms through that interface, but if they do then it might be possible to do OPC - ETL.    

(CID:129407760)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-04 03:23 PM

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc