I have DCE solution. I want a physical notification system like flasher or sounder.
DCE has netbotz 250 in the private network. I want physical alarm notification for all alarms generate by DCE.
Not only for netbotz devices.
(CID:151062767)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:16 PM . Last Modified: 2024-04-03 12:11 AM
Hi,
I always recomend to use the client preferences for activate a sound because any alarma.
I don't know any othe way to make a fisical output from DCE

(CID:151062949)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:16 PM . Last Modified: 2024-04-03 12:11 AM
Could we provide trigger for the DCE alarm through Netbotz 250?
Netbotz has output relay contacts.
(CID:151063186)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:16 PM . Last Modified: 2024-04-03 12:11 AM
No, I don't think so.
Netbotz can activate the relay contacts because any alarm configurated at It self but not for alarms configurated in DCE.
Remember comunication SNMP betwen netbotz and DCE is just for monitoring.
(CID:151063282)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:16 PM . Last Modified: 2023-10-22 02:32 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.