How to implement load-shedding with switched PDUs and DCE?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How to implement load-shedding with switched PDUs and DCE?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
ElectricAvenue
Crewman ElectricAvenue
Crewman

Posted: ‎2024-09-26 07:34 PM

0 Likes
3
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-26 07:34 PM

How to implement load-shedding with switched PDUs and DCE?

Hello,

 

We're upgrading our power setup to a larger Symmetra, and need to implement load-shedding. With many small Smart-UPS units, tier 2/3 loads inherently had less runtime by design, now we need to implement it differently.

This is a necessary part of our operations; we have many Macs and other equipment that is not suitable for PCNS, and we want to guarantee certain, lower-priority racks are shut down based on time-passed or remaining-runtime. In the mean time critical servers and storage would get all the runtime they can get.

 

When we presented this to our Schneider Electric rep, he stated that with DCE and switched PDUs, "they can be configured this way". Now we have those and I'm running tests, and I don't see anywhere in DCE to programmatically control outlets — scripts, macros, rules, etc.  I only see manual outlet control, and reporting rules (email/SNMP). What am I missing?

 

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2024-09-27 11:04 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-27 11:04 AM

Hello @ElectricAvenue,

 

I have reached out to a Sales Engineer to see if they can reach out to you to discuss your setup and what was purchased to discuss any viable options.  Data Center Expert is only a monitoring tool, and does not have any power control functionality that will automatically perform tasks.  It only has the capability of manually controlling outlets on/off as you have already seen.

 

PowerChute Network Shutdown does have an option to run scripts, which may be of use here.  You can read about using "Shutdown Command Files" in the PowerChute Network Shutdown Standard User Guide: https://www.apc.com/us/en/product-range/61933-powerchute-network-shutdown/#documents

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

ElectricAvenue
Crewman ElectricAvenue
Crewman

Posted: ‎2024-10-01 03:53 PM

0 Likes
1
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-01 03:53 PM

Hi Cory,

This is a serious issue. I haven't seen other updates here/in private, what did you hear from the sales engineers?

 

As said, PowerChute Network Shutdown is fully irrelevant since it doesn't support macOS. We also want a solution that controls the outlets, not (just) the operating system, to ensure/force a shutdown. We already invested in the PDUs for this exact reason.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2024-10-03 06:14 PM

In response to ElectricAvenue
0 Likes
0
913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-03 06:14 PM

Hello @ElectricAvenue,

 

Your sales channel partner should have reached out to you or be reaching out to you to discuss further.  If you haven't heard from them, I would recommend reaching out.

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore