HI Team,
We are trying to establish Easy UPS SRV6KL-IN communication with EcoStruxure IT application and facing some challenges in connecting via SNMPV2 and SNMPV3 I have attached logs for your reference.
Easy UPS uses software monitoring application to monitor and control the UPS, we wanted to know what settings we have to perform to establish communication and discover with EcoStruxure It application.
Thanks
Ravikumar Benkond
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-25 06:00 AM
Hi,
I would suggest you to check the following:
1. Is the UPS is in the same network as the IT Gateway?
2. Any firewall that blocks the port for SNMP?
3. Did you check the community string setting when using SNMP V2?
4. Is the options for SNMP V3 settings matches in IT Gateway compared to the settings of the SNMP Card?
You use the SNMP Manager software to check item 3 and 4.
Hope this give some hint.
BR,
TJ.