How to change notifcation policy from default on APC AP7721 & AP4421

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How to change notifcation policy from default on APC AP7721 & AP4421
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:43 AM

0 Likes
6
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:43 AM

How to change notifcation policy from default on APC AP7721 & AP4421

Hello

 

In DCE, how do you change the notification policy from "Default" for automatic alerts on an APC AP7721 & AP4421 automatic transfer switches.

 

Regards,

Brendan.

(CID:148342366)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:43 AM

0 Likes
4
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:43 AM

Dear Brendan,

Can you please refer the tip written on how to manage the DCE Notification policy? I hope it should help you.

https://community.ecostruxureit.com/questions/108825984/data-center-expert---how-to-configure-email-...

https://www.apc.com/us/en/faqs/FA225766/

Regards,

Bala

(CID:148342370)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:43 AM

0 Likes
4
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:43 AM

Dear Brendan,

Can you please refer the tip written on how to manage the DCE Notification policy? I hope it should help you.

https://community.ecostruxureit.com/questions/108825984/data-center-expert---how-to-configure-email-...

https://www.apc.com/us/en/faqs/FA225766/

Regards,

Bala

(CID:148342370)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:42 AM

In response to DCIM_Support
0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:42 AM

Hello Bala,

Thanks for the reply but I didn't find a solution in the links you provided.

I'm probably not asking the question correctly.

The screen shots below might do a better job.

Kind regards,

Brendan.

(CID:148770513)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:42 AM

In response to DCIM_Support
0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:42 AM

Dear Brendan,

Thanks for the screen shots. 

Communication Status Thresholds and any custom created thresholds need to be added manually if a new notification policy is created.

Add Thresholds to a notification policy option allows you to add to a notification policy. It can be default or a new notification policy that you created.

By default, the communication status-status link which you find under Threshold alarm configuration is associated to default notification. If you want to assign this notification policy to a different notification policy, then use the Add Thresholds to a notification policy option shown in your screen shot. 

Note: Device Alarm thresholds can not be added to more than one notification policy. 

If you want to change the Device Alarm thresholds from default notification policy, then please go to the respective Notification policy section-Devices-Choose Devices-Select your ATS product so that it will part of your new notification policy. 

 

 

Please note the following difference Between Threshold Alarms and Device Alarms.  

Device Alarms Configurations: When an alarm occurs on an APC device, StruxureWare Data Center Expert should see the alarm, as long as it occurs for a long enough period of time and does not clear too quickly.  When StruxureWare DCE sees the alarm, it will look to see what Notification policy that the alarm is within and then perform the alarm actions defined within it.

Threshold Alarms Configurations:  Every SNMP/ModbusTCP device that is added into StruxureWare DCE by default will have a Communication Status - Link Status threshold.  This threshold can not be deleted, but it can be disabled.  You can also define other custom thresholds within DCE and associate them to one or more notification policies.  These custom thresholds can be based off of any sensor value that we are pulling in from a unit, whether APC or third party devices.

I also let other community folks to answer you. 

Regards,

Bala

(CID:148770502)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:42 AM

In response to DCIM_Support
0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:42 AM

Hi Bala,

That worked perfectly thanks.

I tried a short email with a device alarm but got a strange result.

I take it I'll have to mess around with macros to get the exact info I need on a short email?

Kind regards,

Brendan.

(CID:148770507)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:42 AM

In response to DCIM_Support
0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2024-04-03 12:42 AM

Dear Brendan,

I am glad that I could help đŸ˜€

Using the Short Message Email, we can limit the characters by specifying the DCE Macros. 

In order to customize email notifications, you would need to use the Short Message Email Option.  Below is a quick how-to guide to create and customiz a new Short Message Email alert. 

1) Open the StruxureWare Data Center Expert client.

2) Alarm Configuration Menu > Manage Alarm Actions.

3) Create...

4) Send Short message Email... > Next.

5) Provide an SMS E-mail Action Name and add in the emails that you would like it to go to. 

6) The Subject and message fields can be customized using a defined list of macros that are available:

  • Alert Macros
  • Identification Macros
  • Location Macros

An example of macro usage with their results is listed below.  Text, including spaces within the email will be kept when the information is emailed out.

 

 

Example of sending short message email Macros usage. 

 

 

 

After creating a custom Short Message Email, remember to associate it to a Notification Policy. 

 

Alert Macros:

Macro

Example

${ALERTTYPE}

HIGHERR

${SENSORTYPE}

TEMP

${SENSORVAL}

60

${ALERTTIME}

Apr 2, 2009 13:01:45

${ALERTSEV}

ERR, WARN-RTN

${SENSORNAME}

Bldg. 3 Door

${ALERT_PROFILE}

Default, Profile #1

${ALERT_LEVEL}

First Alert Level, Second Alert Level

${ISACTIVE?yes?no}

“active” and “cleared”

${USERURL}

http://www.mysite.com

${USERDESC}

“Too high”

${START_TIME}

13:01:45

${RESOLVE_TIME}

13:07:13

${SENSORLUID}

TEMP1

${SENSORGUID}

B000113_TEMP1

${EVENTID}

3E4512C0FE03440F

${ALERTPOD}

My Pod

${ALERTPODSERIAL}

NB007100730114

${ALERTPORT}

Ext1

${CURRENT_ALERT_NUM}

0, 1, 2

${RESOLVEUSERID}

Joeuser

${RESOLVECOMMENT}

“Turned on the A/C”; “Fixed the leak”

 

 

 

Identification Macros:

Macro

Example

${SERIAL}

5A0902V00025

${IP}

192.168.2.23

${HOSTNAME}

isxc.apc.com

${MODEL}

WallBotz 500

${TIMESTAMP}

998885130

${DATE}

27/03/2009

${YEAR}

2009

${MONTH}

3

${DAY}

27

${TIME}

23-30-01

${HOUR}

23

${MIN}

30

${SEC}

1

${VER}

2_6_2-20071031_1658

 

Location Macros:

Macro

Example

${LOCATION}

Test Lab

${ENCLOSURE}

RACK1234

${SLOT}

A23

${ENCRELLOC}

ATUPS

${ROOM}

C-100

${ROOMROW}

AA

${ROOMCOL}

25

${HEIGHT}

60

${BLDG}

205

${FLOOR}

3

${COMPANY}

APC

${ADDRESS1}

132 Fairgrounds Road

${ADDRESS2}

Building 1

${CITY}

W. Kingston

${STATE}

RI

${COUNTRY}

USA

${CONTACT}

J. Smith

${SITE}

West Campus

${NOTES}

IT Closet, Server Room

${LATITUDE}

30° 18’ N

${LONGITUDE}

97° 42’ W

${GPSLOC}

30° 18’ N / 97° 42’ W

 

I hope this helps. 

Regards,

Bala

(CID:148770511)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2023-10-22 02:26 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:44 PM . Last Modified: ‎2023-10-22 02:26 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Š 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of